I have 2 SMART-UPS 1400s. On one system the Agent will not start, the Application event log shows "Communication Not Established" I've moved the cable to both a windows 2003 and a windows xp system. The working agent is on a windows 2000 server system.
I've set the serial port options and can verify with hyperterminal can send/receive commands.
During install of the agent on the failing system, it is detected as a SMART-UPS but the type isadmin ???6 RM XL on COM1. The working one detected the correct type.
Does anyone have a suggestion on how to further debug this?
Thanks,
David
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
I have 2 SMART-UPS 1400s. On one system the Agent will not start, the Application event log shows "Communication Not Established" I've moved the cable to both a windows 2003 and a windows xp system. The working agent is on a windows 2000 server system.
I've set the serial port options and can verify with hyperterminal can send/receive commands.
During install of the agent on the failing system, it is detected as a SMART-UPS but the type isadmin ???6 RM XL on COM1. The working one detected the correct type.
Does anyone have a suggestion on how to further debug this?
Thanks,
David
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
Also make sure that the comm port settings are at 2400, 8, none, 1, Xon/Xoff
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
I switched the cables between the 2 systems and the problem moved with the cable. It seems that I have a bad cable.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
Hello,
If your Smart-UPS is within the 2 year factory warranty, you can call APC at 800-890-4272 to speak to a technical support representative and explain the situation to have a replacement cable mailed out.
If the UPS is out of warranty, the Smart Signaling serial cable can be purchased through our website:
http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=940%2D0024
The serial number off of the UPS will let us know whether the UPS is under warranty or not.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:46 AM . Last Modified: 2024-03-07 11:56 PM
I have 2 SMART-UPS 1400s. On one system the Agent will not start, the Application event log shows "Communication Not Established" I've moved the cable to both a windows 2003 and a windows xp system. The working agent is on a windows 2000 server system.
I've set the serial port options and can verify with hyperterminal can send/receive commands.
During install of the agent on the failing system, it is detected as a SMART-UPS but the type isadmin ???6 RM XL on COM1. The working one detected the correct type.
Does anyone have a suggestion on how to further debug this?
Thanks,
David