PX SYPM10KF controller question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PX SYPM10KF controller question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ksquare_apc
Ensign ksquare_apc
Ensign

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
7
2322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

PX SYPM10KF controller question

Can I get any info on the LED indicators on a PX controller card? I'm looking at the 7 green LEDs, 3 amber LEDs and 1 red LED. I have a module that is trying to tell me something. The green LED by the reset switch is labeled "Supply OK" so that one is obvious. Not so the others. Also, what is the functionality of that Reset button? Thanks.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi Ken,

Support did not know anything about the specifics at the board level - LEDs or reset button.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi Ken,

I asked our 3 phase support and they weren't sure what you were referring to. They did not know what a "controller card" is for a PX and the part number you posted is a UPS Power Module. Can you show a picture of the LEDs or clarify further where you are looking specifically on the system? I thought maybe it was the MIM but the lights for that don't say "Supply OK" on them either. Power Modules also don't have all those LEDs.

Reply

Link copied. Please paste this link to share this article on your social media post.

ksquare_apc
Ensign ksquare_apc
Ensign

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

Hi Angela,

It's what I call a controller card. I don't know what its official name is. Here is a pic of the board with the LEDs shown in their colors.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi Ken,

I asked 3 phase support and they tell me this is the controller board out of the power module itself? They can't/wont release any detail on this as we don't even typically troubleshoot to that level. I got the gist that support does not honestly have access to this information. I assume your UPS is reporting a Power Module fault?

Reply

Link copied. Please paste this link to share this article on your social media post.

ksquare_apc
Ensign ksquare_apc
Ensign

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-02-14 02:32 AM

0 Likes
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-02-14 02:32 AM

Hi Angela,

Yes this is the controller board out of the power module. Bummer that the info isn't available. Those LEDs were put there for some reason. Someone, somewhere at some time knew what they said. No, my UPS is not reporting a fault (at least not on the display because it is not getting through self-test. I thought maybe the LEDs would tell me to check air in the tires or oil in the engine 🙂

Thanks for trying!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi Ken,

You're welcome smile

Reply

Link copied. Please paste this link to share this article on your social media post.

ksquare_apc
Ensign ksquare_apc
Ensign

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-02-14 02:32 AM

0 Likes
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-02-14 02:32 AM

Did you get an answer about that Reset button? Actually I'm not sure how I could reach it even with the lid off but if it is worth it, I'll find a way 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
2320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi Ken,

Support did not know anything about the specifics at the board level - LEDs or reset button.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore