SY80K80F Static Switch Issues, Again

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SY80K80F Static Switch Issues, Again
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
andvari7_apc
andvari7_apc
Cadet

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
1
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-02-14 02:22 AM

SY80K80F Static Switch Issues, Again

Good morning,

I'm having another issue with the Symmetra PX 80 Static Switch:

An 80 [kW] needs a replacement static switch. Can we swap out the old for a new while the unit is running, or do we need to put it into external bypass? I cannot find any information in the manuals about the static switch, let alone detailed instructions as to how to replace it while the unit is still running.

Thank you.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

Hello,

I found this information in our knowledge base. If you have further questions on the specifics, I'd contact 3 phase technical support to avoid a problem during the procedure.

Static Switch Modules on the Symmetra PX 80 and PX 100 may be hot swapped. This procedure is not possible on the Symmetra PX 40 and ISX 20K All-in-one.  

In some cases, the static bypass feature may still be available even though the SSW is reporting as failed. If the alarm is one of the three listed below, then static bypass is available through the Power view (on MIM 17.0 >).

1. Overload in PSU (Severity Level 2)
2. Fan_Fault (Severity Level 2)
3. Heatsink over temp (Severity Level 2)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:29 PM . Last Modified: ‎2024-01-31 02:55 AM

Hello,

I found this information in our knowledge base. If you have further questions on the specifics, I'd contact 3 phase technical support to avoid a problem during the procedure.

Static Switch Modules on the Symmetra PX 80 and PX 100 may be hot swapped. This procedure is not possible on the Symmetra PX 40 and ISX 20K All-in-one.  

In some cases, the static bypass feature may still be available even though the SSW is reporting as failed. If the alarm is one of the three listed below, then static bypass is available through the Power view (on MIM 17.0 >).

1. Overload in PSU (Severity Level 2)
2. Fan_Fault (Severity Level 2)
3. Heatsink over temp (Severity Level 2)
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.