I am running PCNS 4.0 on a bunch of OS X systems and need user notifications.
Doing this through the web interface for each event is cumbersome (Configure Events - Notification - Enable User Notification - Apply).
Can user notification be configured through pcnsconfig.ini or command line?
Stefan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:48 AM . Last Modified: 2024-02-29 11:00 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:48 AM . Last Modified: 2024-02-29 11:00 PM
Stephen,
User Notification cannot be set using the .ini file or command line.