NMC2 firmware enhancement request for HTTP->HTTPS redirect

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC2 firmware enhancement request for HTTP->HTTPS redirect
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
3
2314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

NMC2 firmware enhancement request for HTTP->HTTPS redirect

On all of the older hw02 products, if HTTP is not enabled (and HTTPS is), browsing to the device's HTTP page returns:

Protected Object. 
This object on the APC Management Web Server is protected and requires a secure socket connection.
Click here to use a secure connection.

On the NMC2 (hw05) products, browsing to the devices HTTP page returns:

Protected Object
This object on the  APC Management Web Server is protected.

In a future firmware release, could that page be changed to include a link to the device's HTTPS page as is done on the older cards? If so, it will be important to either replicate the hw02 functionality (the redirect URL contains card's IP address) or to always go to the FQDN form of the hostname as configured on the card. Otherwise (assuming the card has an SSL certificate issued to device.example.com), browsing to http://device (without the FQDN) will redirect to https://device and generate a "The security certificate presented by this website was issued for a different website's address." or similar error, since the certificate is issued for the FQDN and the user's browser is using the short-form name. I suspect that is why the hw02 implementation always redirects to the IP address.

Note that this is a cross-platform issue (UPS, PDU, ATS, etc. - anything that uses the NMC2 hardware).

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-08 12:49 AM . Last Modified: ‎2024-02-29 10:59 PM

0 Likes
0
2313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:49 AM . Last Modified: ‎2024-02-29 10:59 PM

If I had to guess, I think the concern is that redirecting from HTTP to HTTPS would only offer protection from passive attackers. Active ones can sit in between and keep the connection at HTTP. Not doing the redirect doesn't directly protect against this: attackers could still intercept the HTTP connection and proxy it to HTTPS, however if HTTP ordinarily doesn't work, hopefully nobody would be making an HTTP connection in the first place.

That said, a friendlier option is to use a permanent redirect so the browser autocompletes with the https:// version.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
2313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Hi Terry,

They had removed this for security reasons. When NMC2 came out, we had a lot of questions on it but the reason is that with the link there on the HTTP page, it gives the user the direct link and configured port number to get to the HTTPS page and that is why we felt it was a security issue and not a good idea to put a hyperlink on the HTTP page since it could get a malicious user that much going closer to gaining access. I can ask about it again but I don't think the opinion has changed unless you can give me any ideas why it wouldn't be a security issue. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:49 AM . Last Modified: ‎2024-02-29 10:59 PM

0 Likes
0
2313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:49 AM . Last Modified: ‎2024-02-29 10:59 PM

I'm not sure I follow this - if bad guys are able to access http://device.example.com (even to get the page they see now), they can just try https://device.example.com, assuming the device is configured to use the default port. And it is probably a bad idea to have these devices accessible from the whole Internet, anyway.

How about this, which would actually improve that sort of security: Instead of having checkboxes for HTTP, make it 3-choice radio buttons, with the following options: a) no response (don't listen to the port and don't serve any pages), b) simple error page (the current behavior), or c) Error page with redirect to HTTPS. There probably isn't any reason to have an error or redirect page if the user tries HTTPS and it is disabled, since the user would have previously needed to enable HTTPS and install a certificate, which would be rather silly just to tell people to use HTTP.

The existing canned response on the HTTP port discloses that the device is an APC / Schneider management card, and the major version can be inferred by whether the user sees the blue or green page. That is enough that if an exploit against the firmware is disclosed, it is trivially easy to scan the whole IPv4 address space and find APC devices.

And, by the way, the NMC2 web server will serve content out of its images directory to logged-out HTTP users when HTTP is disabled. For example, http://device.example.com/images/good.gif, which is not used in the error page. The NMC2 does protect its other pages from logged-out users. However, it might be possible to infer more information than the fact that it is an APC card and the major version (which the default error page easily reveals) by seeing if a particular image exists in that directory.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-08 12:49 AM . Last Modified: ‎2024-02-29 10:59 PM

0 Likes
0
2314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:49 AM . Last Modified: ‎2024-02-29 10:59 PM

If I had to guess, I think the concern is that redirecting from HTTP to HTTPS would only offer protection from passive attackers. Active ones can sit in between and keep the connection at HTTP. Not doing the redirect doesn't directly protect against this: attackers could still intercept the HTTP connection and proxy it to HTTPS, however if HTTP ordinarily doesn't work, hopefully nobody would be making an HTTP connection in the first place.

That said, a friendlier option is to use a permanent redirect so the browser autocompletes with the https:// version.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore