Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

PowerChute not working as expected?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute not working as expected?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
yomark_apc
Crewman yomark_apc
Crewman

Posted: ‎2021-07-08 12:48 AM

0 Likes
8
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

PowerChute not working as expected?

This was originally posted on APC forums on 6/29/2015


Hello People,

 

At our company we have several off-site locations running with a Vmware ESX server connected to a APC UPS(several different types).

(We've never really tested the UPS shutdown sequence though, so that's what I'm doing now).

On the ESX server I've created a separate PowerChute VM(installed pcns310win-x86-64), and configured it(Powerchute setup) without problems(I thought).

First step in wanted to take: shut down the Vmware host when UPS runtime is less then 900 seconds.

So I configured to shutdown using the "Runtime remaining below threshold", and set it to 900 seconds.

Now the problem is: it just does not do anything. When I pull the power cord from the UPS, it immediately logs an "UPS has switched to battery power" event in Powerchute. But nothing happens when it passes the 900seconds barrier(15 minutes as shown in the UPS interface itself). I let it continue all the way until there was only 1 minute left in the UPS(even logs critical "Low Battery" events in the minutes before that the logs), but no shutdown was initiated.

Now, I do not understand I lot of options in the UPS configuration thoroughly.

 

What am I doing wrong? I've included some screenshots with the settings i've made.

Thanks in advance!

--Mark

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • esx
  • PowerChute
  • threshold
  • vmware
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
yomark_apc
Crewman yomark_apc
Crewman

Posted: ‎2021-07-08 12:48 AM

0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

This was originally posted on APC forums on 7/7/2015


Installed the VA version 4 now. Configured exactly the same settings. Going to test it later.

See Answer In Context

Reply
Share
Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:48 AM

0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

This reply was originally posted by Bill on APC forums on 6/29/2015


Hi,

Are the host ESX or ESXi? IF the hosts are ESX you should install PowerChute on the ESX host. If the hosts are ESXi then you should install the PCNS appliance.

Here is a link to PCNS for ESX and the Appliance.

You ahould review PCNS VMware Users Guide.

 

Reply
Share
yomark_apc
Crewman yomark_apc
Crewman

Posted: ‎2021-07-08 12:48 AM

0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

This was originally posted on APC forums on 6/30/2015


Bill, thanks for you reply!

We're using ESXi(5.5+).

 I'm not a big fan of virtual appliances, they are hard to maintain, often impossible to update, hard to keep secure, and always an exceptions of the rest of the environment(Windows/specific Linux version/ etc..). And it is an OS you should maintain nonetheless. so that why I specifically chose not to use the VA.

 Also, I think that running PCNS on standard Windows/Linux is not very different from running the same thing on a VA(only the VA is a lazy way). It's just Powerchute on a trimmed down linux, right? The same questions remain.

 Is there some way I can troubleshoot this? We have 20 ESXi servers running on 20 APC UPS, all configured in the same way. However, this is the first time we really tested it(in a way to really drain the battery). I used the "PowerChute Network Shutdown v3.1" Installation Guide(number 990-2838H-001, Windows, Linux, Hyper-V, Vmware combined).

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:48 AM

0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

This reply was originally posted by Bill on APC forums on 6/30/2015


Mark,

Your configuration is not officially supported but it should work. You need to configure PCNS with a standalone host. Provide the host credentials, and the host must be fully licensed (not the free license). You must configure the host to power down the VMs (Kbase FA159688). Also, each VM must have VMware tools installed for them to be shut down by the host.

Reply
Share
yomark_apc
Crewman yomark_apc
Crewman

Posted: ‎2021-07-08 12:48 AM

0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

This was originally posted on APC forums on 7/2/2015


Tnx Bill. I did all that. Everything is configured as I think it should be. So 1 PowerChute installation for every ESX host/UPS.

Powerchute should give the command to ESX to power down.The ESX host will power down the VM's, when the power comes back the host will power on, and the VM's will start again.

This all seems to work "kinda". Powerchute communicates with ESXi and communicates with the UPS(see logs/screenshots).

The problem is is that "Runtime remaining below threshold" does absolutely nothing, see logs/screenshots. So when i pull tje plug, Powerchute sees that the UPS is running on battery, and in the UPS webinterface i eventually see the runtime dropping below the 900 seconds(configured threshold in Powerchute), but nothing happens.

How does this work under the hood(Powerchute pulls this runtime data from the UPS right?)?

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:48 AM

0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

This reply was originally posted by Bill on APC forums on 7/3/2015


Mark,

As I wrote earlier this is not supported.

You should look in the folder that PowerChute is installed in and there will be an error log. Review the error log. It should give an indication as to what is happening when the threshold is met. Also, the screenshot shows that the UPS hit low battery. PowerChute should start a shutdown as soon as low battery is met. Since it did not that looks to me as though there is a communications issue with the host and you should see that in the error log.

Reply
Share
yomark_apc
Crewman yomark_apc
Crewman

Posted: ‎2021-07-08 12:48 AM

0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

This was originally posted on APC forums on 7/3/2015


Thank for the reply Bill. 

I will have a look at the logs.

So you're saying the Virtual appliance the only supported way of shutting down a standalone ESXi host(in de the case that there are no physical machines)?

The manual I have(Installation Guide v3.1) says it's recommended to use the VA, but nothing idicates it's unsupported. Of course I do not want a unsupported situation, but I do not want a virtual appliance either(and certainly want no vMA, don't know if thats still required for the 4.0 VA). 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:48 AM

0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

This reply was originally posted by Bill on APC forums on 7/6/2015


Mark,

On 7/3/2015 10:03 AM, Mark said:

So you're saying the Virtual appliance the only supported way of shutting down a standalone ESXi host(in de the case that there are no physical machines)?

If you don't want to install the Appliance or a vMA the other option is to install PowerChute on a standalone Windows system (none VM) and configure it to power down the ESXi host.

On 7/3/2015 10:03 AM, Mark said:

The manual I have(Installation Guide v3.1) says it's recommended to use the VA, but nothing idicates it's unsupported. Of course I do not want a unsupported situation, but I do not want a virtual appliance either(and certainly want no vMA, don't know if thats still required for the 4.0 VA). 

PCNS 4.0 is the same as 3.1. We offer the Appliance, vMA or standalone options.

Reply
Share
yomark_apc
Crewman yomark_apc
Crewman

Posted: ‎2021-07-08 12:48 AM

0 Likes
0
844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:48 AM

This was originally posted on APC forums on 7/7/2015


Installed the VA version 4 now. Configured exactly the same settings. Going to test it later.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc