PowerChute not working as expected?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute not working as expected?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:01 PM

0 Likes
8
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:01 PM

PowerChute not working as expected?

Hello People,

 

At our company we have several off-site locations running with a Vmware ESX server connected to a APC UPS(several different types).

(We've never really tested the UPS shutdown sequence though, so that's what I'm doing now).

On the ESX server I've created a separate PowerChute VM(installed pcns310win-x86-64), and configured it(Powerchute setup) without problems(I thought).

First step in wanted to take: shut down the Vmware host when UPS runtime is less then 900 seconds.

So I configured to shutdown using the "Runtime remaining below threshold", and set it to 900 seconds.

Now the problem is: it just does not do anything. When I pull the power cord from the UPS, it immediately logs an "UPS has switched to battery power" event in Powerchute. But nothing happens when it passes the 900seconds barrier(15 minutes as shown in the UPS interface itself). I let it continue all the way until there was only 1 minute left in the UPS(even logs critical "Low Battery" events in the minutes before that the logs), but no shutdown was initiated.

Now, I do not understand I lot of options in the UPS configuration thoroughly.

 

What am I doing wrong? I've included some screenshots with the settings i've made.

Thanks in advance!

--Mark

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • esx
  • PowerChute
  • threshold
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Installed the VA version 4 now. Configured exactly the same settings. Going to test it later.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Hi,

Are the host ESX or ESXi? IF the hosts are ESX you should install PowerChute on the ESX host. If the hosts are ESXi then you should install the PCNS appliance.

Here is a link to PCNS for ESX and the Appliance.

You ahould review PCNS VMware Users Guide.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Bill, thanks for you reply!

We're using ESXi(5.5+).

 I'm not a big fan of virtual appliances, they are hard to maintain, often impossible to update, hard to keep secure, and always an exceptions of the rest of the environment(Windows/specific Linux version/ etc..). And it is an OS you should maintain nonetheless. so that why I specifically chose not to use the VA.

 Also, I think that running PCNS on standard Windows/Linux is not very different from running the same thing on a VA(only the VA is a lazy way). It's just Powerchute on a trimmed down linux, right? The same questions remain.

 Is there some way I can troubleshoot this? We have 20 ESXi servers running on 20 APC UPS, all configured in the same way. However, this is the first time we really tested it(in a way to really drain the battery). I used the "PowerChute Network Shutdown v3.1" Installation Guide(number 990-2838H-001, Windows, Linux, Hyper-V, Vmware combined).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Mark,

Your configuration is not officially supported but it should work. You need to configure PCNS with a standalone host. Provide the host credentials, and the host must be fully licensed (not the free license). You must configure the host to power down the VMs (Kbase FA159688). Also, each VM must have VMware tools installed for them to be shut down by the host.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Tnx Bill. I did all that. Everything is configured as I think it should be. So 1 PowerChute installation for every ESX host/UPS.

Powerchute should give the command to ESX to power down.The ESX host will power down the VM's, when the power comes back the host will power on, and the VM's will start again.

This all seems to work "kinda". Powerchute communicates with ESXi and communicates with the UPS(see logs/screenshots).

The problem is is that "Runtime remaining below threshold" does absolutely nothing, see logs/screenshots. So when i pull tje plug, Powerchute sees that the UPS is running on battery, and in the UPS webinterface i eventually see the runtime dropping below the 900 seconds(configured threshold in Powerchute), but nothing happens.

How does this work under the hood(Powerchute pulls this runtime data from the UPS right?)?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Mark,

As I wrote earlier this is not supported.

You should look in the folder that PowerChute is installed in and there will be an error log. Review the error log. It should give an indication as to what is happening when the threshold is met. Also, the screenshot shows that the UPS hit low battery. PowerChute should start a shutdown as soon as low battery is met. Since it did not that looks to me as though there is a communications issue with the host and you should see that in the error log.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Thank for the reply Bill. 

I will have a look at the logs.

So you're saying the Virtual appliance the only supported way of shutting down a standalone ESXi host(in de the case that there are no physical machines)?

The manual I have(Installation Guide v3.1) says it's recommended to use the VA, but nothing idicates it's unsupported. Of course I do not want a unsupported situation, but I do not want a virtual appliance either(and certainly want no vMA, don't know if thats still required for the 4.0 VA). 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Mark,

On 7/3/2015 10:03 AM, Mark said:

So you're saying the Virtual appliance the only supported way of shutting down a standalone ESXi host(in de the case that there are no physical machines)?

If you don't want to install the Appliance or a vMA the other option is to install PowerChute on a standalone Windows system (none VM) and configure it to power down the ESXi host.

On 7/3/2015 10:03 AM, Mark said:

The manual I have(Installation Guide v3.1) says it's recommended to use the VA, but nothing idicates it's unsupported. Of course I do not want a unsupported situation, but I do not want a virtual appliance either(and certainly want no vMA, don't know if thats still required for the 4.0 VA). 

PCNS 4.0 is the same as 3.1. We offer the Appliance, vMA or standalone options.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

0 Likes
0
3454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:48 AM . Last Modified: ‎2024-02-29 11:00 PM

Installed the VA version 4 now. Configured exactly the same settings. Going to test it later.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore