Posted: 2021-06-29 08:53 AM . Last Modified: 2024-03-12 01:35 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:53 AM . Last Modified: 2024-03-12 01:35 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:53 AM . Last Modified: 2024-03-12 01:34 AM
Hi,
You will find a description of how to configure PCNS for multiple sites in Application Note 180. The recommendation is to have PCNS running on a stand alone Windows system at each site. vCenter Server should also be running on a stand alone Windows system at one of the four sites. PCNS and vCenter can be running as VMs but that is not the recommended configuration.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:53 AM . Last Modified: 2024-03-12 01:34 AM
Hi,
You will find a description of how to configure PCNS for multiple sites in Application Note 180. The recommendation is to have PCNS running on a stand alone Windows system at each site. vCenter Server should also be running on a stand alone Windows system at one of the four sites. PCNS and vCenter can be running as VMs but that is not the recommended configuration.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:53 AM . Last Modified: 2024-03-12 01:34 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:53 AM . Last Modified: 2024-03-12 01:34 AM
Hi,
thank you for your quick response.
We now deployed a seperate PCNS Appliance for every site without physical hosts and a PCNS Client with VMware Support for every site that has a physical host.
Unfortunately I wont have the chance to test the deployment soon.
But I will report the outcome when tests have been made.
Kind Regards