APC SUA3000RM2U dead...?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SUA3000RM2U dead...?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:37 AM

0 Likes
7
2018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:37 AM

APC SUA3000RM2U dead...?

Dear Forum,

I have an APC SUA3000RM2U, which is obviously older, and has been sitting on a shelf for a few years but was pulled from a working environment.   Upon applying power to the device it exhibits absolutely no reaction whatsoever - not a single light comes on, no clicks or sounds, nothing - it's like I've plugged a rock into the power outlet.  I've checked everything I can think of, pressed all the buttons, flipped the breaker on the back, etc. to no avail.  I've also let it sit on power for 24 hours.

Should this device exhibit *some* reaction to being powered?  I don't want to buy a battery pack for it until I'm sure that will fix the problem I'm perceiving.  And if I'm missing something simple, like a fuse I didn't notice, please let me know.

Thanks in advance for any help,

J.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • dead
  • fault
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:37 AM

0 Likes
0
2018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:37 AM

Typically, SUA units do not require the battery to turn on. Though, if there is no DC voltage present anywhere in the system, you may need batteries to jump start it.

Was the battery in this system stored connected or disconnected? Can you measure the voltage on the existing battery pack?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:37 AM

0 Likes
0
2019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:37 AM

Typically, SUA units do not require the battery to turn on. Though, if there is no DC voltage present anywhere in the system, you may need batteries to jump start it.

Was the battery in this system stored connected or disconnected? Can you measure the voltage on the existing battery pack?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:37 AM

0 Likes
0
2018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:37 AM

It was stored connected and I'm certain it is completely drained.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:35 AM

0 Likes
0
2018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:35 AM

From my experience, I do think it is worth a try to "jumpstart" it with new batteries, preferably if you're able to return the batteries if the UPS does happen to be the issue. I can't be sure which it is since the batteries are likely completely shot due to being stored connected and not periodically recharged.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

0 Likes
0
2018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

I may try to jury-rig a 48v source and jump-start it with that first...  at $260+, the battery pack is a big risk.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

0 Likes
0
2018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

OK - it worked.  I stacked 5 9v batteries and used a pair of test leads to energize the input connector from the battery pack.  Ping, on it came.  Thank you very much - it's dinging "Replace Battery" even with the old pack connected, so I'm going to order a new battery pack.

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

0 Likes
0
2018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

Final note - new battery pack received and installed, everything working perfectly.  Thanks again.  smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

0 Likes
0
2018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

Glad to hear. Thanks for the follow up!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore