PCNS issued shutdown to VMs and ESXi within 5 seconds of being on battery - why?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS issued shutdown to VMs and ESXi within 5 seconds of being on battery - why?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
stanj
Lieutenant JG stanj
Lieutenant JG

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
5
761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

PCNS issued shutdown to VMs and ESXi within 5 seconds of being on battery - why?

We needed to switch the UPS from a power strip unit to a building wall outlet to see if it would remove  Site Wiring Fault messages appearing in the APC logs..

 

When we unplugged the UPS from the power strip and connected to the wall, PCNS started to shut down the VMs and the host.

 

 I am m not sure why, because it was on battery for about 4 seconds then back to building power via the wall outlet. So I am not sure why PCNS received an alert and PCNS did the shutdown?

 

The NMC Shutdown Settings are............

 

Shutdown:

 

  Low Battery Duration 15 min

  Max Required Delay     6 Min

  Basic Low Battery Duration 600 sec

 

Duration of Shutdown

 

    Sleep  0.0 hours

 

Sync Control Shut:

 

  Shutdown Delay            600 sec

  Return Delay                     10 sec

 

NMC status of the batteries shows there is 24 minutes of run time remaining.

 

PCNS Events are only set to log events.

 

Below are some of the messages seen in the log

10:15:22 Low Battery Condition occurred

10:15:22 Shutdown Sequence Started on ESXi

10:15:23 Low Battery Condition Solved

10:15:24 UPS Critical: Low Battery resolved on host ESXi

10:15:24 Starting Maintenance Mode task on host ESXi

10:15:24 Shutting Down VMs

10:15:26 UPS no longer running on battery power or output power has been turned on

10:15:40 Battery is discharged

10:15:56 Battery has charged

10:16:17 Battery is discharged

10:16:21 Battery has recharged

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

Hi,

I cannot say for sure but it is possible by disrupting ground the UPS reported the wrong runtime momentarily. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

Hi,

The log show that the UPS reported a low battery state at 10:15:22 so PCNS started the shut down process. A low battery event is treated as a critical event so by default PowerChute will trigger a shutdown sequence. Even though the event cleared a second later the shutdown cannot be disabled for this events to prevent catastrophic system failure. 

Reply

Link copied. Please paste this link to share this article on your social media post.

stanj
Lieutenant JG stanj
Lieutenant JG

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

What would cause a Low Battery? 

This is a new system and after restarting, it shows 25min of battery life.

I am also seeing several messages in the NMC log  about distorted input and switching back and for to battery, like

11/14

   6:40:13  UPS: on battery in response to distorted input

   6:40:14  UPS: no longer on battery 

11/19

   7:57:55  UPS: on battery in response to distorted input

   7:57:56  UPS: no longer on battery

   8:03:23  UPS: on battery in response to distorted input

   8:03:25  UPS: no longer on battery

   20:13:53  UPS: on battery in response to distorted input

   20:13:24  UPS: no longer on battery

PCNS has similar entries in its' log

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

Hi,

The low battery setting on the NMC is at 15 minutes. When the UPS switched to battery and dropped below 15 minutes of runtime the shutdown was triggered. I cannot say why when restarted the UPS reports 25 minutes of runtime. It may have recharged or it may have only momentarily fallen below the threshold but the log shows it reported low battery so PCNS trigger the shutdown. 

Reply

Link copied. Please paste this link to share this article on your social media post.

stanj
Lieutenant JG stanj
Lieutenant JG

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

The UPS was switched to battery for only 5 seconds when the source was moved from power strip to a wall oulet.  How could the battery have dropped below 15 minutes?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-12 12:55 AM

Hi,

I cannot say for sure but it is possible by disrupting ground the UPS reported the wrong runtime momentarily. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of