PowerChute Business Edition Installation Options

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Business Edition Installation Options
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
4
685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

PowerChute Business Edition Installation Options

Can I install PowerChute on my laptop and connect to all of the UPS's on my network (not necessarily all at once!)?

We have a mix of serial and USB connectivity on the UPS's.

Thanks in advance.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

Hi,

You cannot communicate with multiple UPS using the same PowerChute Agent. To communicate with different UPS you will need to stop the apcpbeagent service, connect the cable to the new UPS, then restart the service. NOTE: This will only work if the UPSs are of the same family. If the UPS are SMT, SMX, SRT, SURTD, SMC those will all work with the same PowerChute Agent. If the UPS are SU, SUA, SURT, SURTA those will all work with the same PowerChtue Agent. You cannot switch between a SUA and SMT and have communications work. In that scenario you need to uninstall and reinstall the Agent.

The way PowerChute Business Edition works is, the Agent is responsible for communications with the UPS. The PowerChute Server is responsible for gathering information from the Agents and the PowerChute Console is the GUI. You can us the PowerChute Server to view multiple Agent but each Agent needs to be dedicated to a single system. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

Hi,

On 11/17/2017 6:29 AM, Richard said:

Can I install PowerChute on my laptop and connect to all of the UPS's on my network (not necessarily all at once!)?

Are all of the UPS connected to systems that are running PowerChute Business Edition Agent? If so then yes. You can connect to the Agent over the network by entering https://:6547 Example https://192.168.1.10:6547

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

Excellent, thanks Bill.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

0 Likes
0
685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:55 AM

I want to be able to manage all UPS's from a single server.

I've installed the PCBE server, agent and console on the candidate management server and plugged two of our three of the UPS's into this server via USB. When launching the console, I can only see one of the UPS's plugged into the management server.

How do I get it to display both of them?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

0 Likes
0
685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:24 PM . Last Modified: ‎2024-03-12 12:54 AM

Hi,

You cannot communicate with multiple UPS using the same PowerChute Agent. To communicate with different UPS you will need to stop the apcpbeagent service, connect the cable to the new UPS, then restart the service. NOTE: This will only work if the UPSs are of the same family. If the UPS are SMT, SMX, SRT, SURTD, SMC those will all work with the same PowerChute Agent. If the UPS are SU, SUA, SURT, SURTA those will all work with the same PowerChtue Agent. You cannot switch between a SUA and SMT and have communications work. In that scenario you need to uninstall and reinstall the Agent.

The way PowerChute Business Edition works is, the Agent is responsible for communications with the UPS. The PowerChute Server is responsible for gathering information from the Agents and the PowerChute Console is the GUI. You can us the PowerChute Server to view multiple Agent but each Agent needs to be dedicated to a single system. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of