PCNS - Low runtime shutdown, service and failure to reboot

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS - Low runtime shutdown, service and failure to reboot
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:26 PM

0 Likes
5
1939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:26 PM

PCNS - Low runtime shutdown, service and failure to reboot

Hello.

I've recently started using an AP9617 in one of our SUA3000s.

I have PCNS installed on two servers, the idea being that they then run a script to remotely shut down all the other servers (shutdown -m etc etc) - they both attempt to shut down everything for redundancy purposes - I have a shutdown event configured on them for "On Battery" with a delay of 60sec, and a cmd file configured within "Configure shutdown" with 30 seconds allowed to run.

These two servers are then supposed to restart once power is restored with a 5 minute delay. I have attempted to do this by setting the "Return delay" on the mgmt card to 300 seconds.

***

Two nights ago a power event occurred. According to the log, a low battery condition occurred 14 seconds later which immediately signalled a shutdown. The script to gracefully shutdown all servers failed. Although the UPS restarted after approximately 300 seconds, the servers did not.

***

So, my questions:
1) How do I stop a shutdown occurring on a "low battery" condition, OR how do I prevent a low battery condition from occurring so quickly? (I am NOT going to reduce the load, please don't bother suggesting it)

2) Why did my script fail? This same script worked fine with PCBE. My guess is that it was because the PCNS service (PowerChute Network Shutdown Group 1?) was running as local system which of course doesn't have authority to shutdown other machines? Is there anything else?

3) Why didn't the 2 servers restart when power was restored? Do I need to configure this within BIOS?

Thanks
//Rob

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 07:55 AM . Last Modified: β€Ž2024-03-07 10:25 PM

0 Likes
0
1938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:55 AM . Last Modified: β€Ž2024-03-07 10:25 PM

"Safety buffer"? I thought the idea of having a managed system was that -you- configure how it works, not some piece of software that believes itself to be cleverer than you? My 2C πŸ™‚

Anyway.
Reports 5 minutes of runtime, which is actually achieved aswell in a power failure - I've timed it.
UPS was also calibrated fully 2 months ago.
Batteries are a little old - 2005, but 5 minutes is sufficient to shutdown the equipment with a 60 sec delay so I see no reason to replace them yet.

I've opened this as a call with APC, but still any ideas welcomed - I'm expecting them to tell me to reduce the load or replace the battery...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:26 PM

0 Likes
0
1938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:26 PM

bump

Really can't have the PDC and SDC shutting themselves down because of a 14 second powercut.

Any more ideas or does anyone from APC have anything to say?

This is an SUA3000RM with half load.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:26 PM

0 Likes
0
1938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:26 PM

Low battery is a default shutdown setting. It's actually configured on the Network Management Card, not PCNS. It's the configuration for Low Battery Duration... in other words, how much time is left before the UPS shuts off. The default is 2 minutes, but that can be increased. You don't have to do anything configuration wise for PCNS to shutdown at low battery, just look at the shutdown settings portion of PCNS.

You're probably dead on as to why the script didn't work. Not having the correct access will cause this and is a common problem.

You're right about the bios as well. APC's software is designed to shutdown the server and put the UPS into sleep mode. When power restores, the UPS turns back on and provides power to the outlets. You need to configure in the systems bios settings to turn on when power is present.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:26 PM

0 Likes
0
1938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:26 PM

Thanks EZ.

I think you've answered questions 2 and 3 there. Unfortunately I can't test them without taking down our PDC, but time will tell!

The low battery duration however:

If I increase the low battery duration, my understanding is that I am increasing the time the UPS believes is required for its equipment to shutdown properly, which would cause it to start shutdown as soon as power fails. Indeed, if I increase it to 27 minutes (currently on 2 mins), its status changes to "batteries discharged".

More ideas please?

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:25 PM

0 Likes
0
1938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:54 AM . Last Modified: β€Ž2024-03-07 10:25 PM

Hmm I think I didn't read that properly the first time when you asked "how do I stop the low battery shutdown."

You can't disable low battery shutdown, it's there as a safety buffer.

What do you have for runtime on the unit? With half load, you certainly should have more than 17 seconds before low battery occurs, so that tells me there is a problem somewhere.

Message was edited by: EZ Button

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 07:55 AM . Last Modified: β€Ž2024-03-07 10:25 PM

0 Likes
0
1939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:55 AM . Last Modified: β€Ž2024-03-07 10:25 PM

"Safety buffer"? I thought the idea of having a managed system was that -you- configure how it works, not some piece of software that believes itself to be cleverer than you? My 2C πŸ™‚

Anyway.
Reports 5 minutes of runtime, which is actually achieved aswell in a power failure - I've timed it.
UPS was also calibrated fully 2 months ago.
Batteries are a little old - 2005, but 5 minutes is sufficient to shutdown the equipment with a 60 sec delay so I see no reason to replace them yet.

I've opened this as a call with APC, but still any ideas welcomed - I'm expecting them to tell me to reduce the load or replace the battery...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore