PCNS 3.1 with VMware 5.5 issues

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS 3.1 with VMware 5.5 issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

0 Likes
8
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

PCNS 3.1 with VMware 5.5 issues

Hi,

I am trying to set up PCNS 3.1 with VMware 5.5.

I have a setup identical to setup A of Application Note 180: Single UPS with NMC, physical server with PCNS, two host cluster with vCenter running in a VM on the cluster. I did not install the VMA, since I don’t believe it’s necessary in this setup. Or is it?

I created an AD user with which I can login to the vCenter server or to either host using the vCenter client.

I checked that PCNS correctly detects the host on which the vCenter VM is running.

All timeouts are default.

When I test the shutdown sequence, I get the following:

10/16/2014 14:40:28 Shutting down Host 10.10.10.102.

10/16/2014 14:40:26 Shutting down Host 10.10.10.103.

10/16/2014 14:40:02 Shutting down physical machine that PowerChute is running on.

10/16/2014 14:40:00 Shutting down Host 10.10.10.103.

10/16/2014 14:40:00 Exit maintenance mode: mp-esx2.jaga.local.

10/16/2014 14:36:00 Shutting down VMs on Host mp-esx2.jaga.local.

10/16/2014 14:36:00 Enter maintenance mode: mp-esx2.jaga.local.

10/16/2014 14:35:59 Shutting down VMs on Host mp-esx3.jaga.local.

10/16/2014 14:35:59 Enter maintenance mode: mp-esx3.jaga.local.

10/16/2014 14:35:59 UPS critical event: On Battery occurred on Hosts: mp-esx3.jaga.local, mp-esx2.jaga.local.

So there’s mainly two issues:

1. No mention of a graceful shutdown of the vCenter server. In the server’s logs I get “The system has rebooted without cleanly shutting down first.”.

2. The physical PCNS server is shut down before the two VMware hosts.

I tried entering the vCenter server IP instead of its hostname, but this did not solve the issue.

Since the vCenter server wasn’t shutdown cleanly, the VMs are not automatically started when power is restored.

What am I doing wrong here?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • pcns
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:46 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:46 PM

Hi Bill,

DNS is running on two DC’s, both virtual machines. One of them was indeed running on the cluster that was being shut down!

I entered the VMware hosts’ IPs into the hosts file on the PCNS server and now the shutdown sequence seems OK!

Now all I have to do is change the ”on battery” event to a “battery remaining” and test the startup procedure as well.

Thanks for your help!

Best regards,

Wouter

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

Hi,

When you look at VMware Host Protection page in PCNS does it display the vCenter icon showing the host that vCenter is running on? If not PCNS will power down vCenter the same as any other VM. In most cases the cause for PCNS not to recognize vCenter is running as VM is because VMware Tools was not installed on the VM. Installing VMware Tools on the the VM vCenter is running on should resolve your issue.

2517_pastedImage_1.png

If after adding VMware Tools to the VM if you are still having an issue please follow the instructions in Knowledge Base (Kbase) document FA230514 to put PCNS into debug mode and send error.log file for review after rerunning the shutdown test.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

Hi,

Thank you for your response.

PCNS shows the vCenter's location just fine:

2519_pcns.jpg

While troubleshooting, I even tried to move the vCenter server to the other host to see if this change was reflected in the PCNS interface, and that worked fine.

I gathered the requested error-debug.log and attached it to the case.

Best regards,

Wouter

Attachments
error-debug.log.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

Hi,

Did the host not shutdown? The error log does not show any issue with the shutdown process of the hosts. Also, may I see a copy of pcnsconfi.ini file.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:09 AM . Last Modified: ‎2024-03-04 11:47 PM

Hi Bill,

In this case only one of the hosts (the one without the vCenter) did shut down.

vCenter server was not shut down, the host it was running on was not shut down.

During testing (this is the fifth run) I’ve had some other results as well, but the main issue seems to be that PCNS fails to shut down the vCenter server.

Please find the requested file in attachment.

Best regards,

Wouter

Attachments
pcnsconfig.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:47 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:47 PM

Hi,

From the logs it shows that PCNS not being able to locate the VCSA VM and its host. It is also not shutting down any of the ESXi hosts prior to local OS shutdown. The ESXi host that is being shut down is actually being shut down using a check that occurs after the local OS shutdown is triggered.

Is it possible to attach the VirtualizationFileStore.properties file?

What is the name of the VM running VSCA?

You may have a machine that is using the same IP address (even if one of them is powered off), this can prevent PCNS from locating the vCenter Server VM and its host.

There is an interface that you can use on vCenter Server called the Managed Object Browser that allows you to check if everything is set-up correctly or if there are problems. It can be accessed viahttps:///mob. You need to log in as a VMware admin.

To check if vCenter Server IP/Hostname/FQDN can be located by what is stored in pcnsconfig.ini for vCenter Server.

Once in MOB. you need to click on theContentLink. Once in the Content Link, click on the SearchIndex link.

If you have added vCenter Server using the IP address - selectFindByIP

In the FindByIP screen, clear the value under datacenter, enter the IP address and set vmSearch boolean "true".

Click Invoke Method.

If the IP address is found in the Inventory you should get a return value and a ManagedObjectReference which will show the VM (the VM name will appear beside it - note that this is the name as it appears in the vCenter Server Inventory, it may not be the same as the IP/FQDN.).

You can click on the MOR reference link  for or more information about the VM (if its found). When you get the MOR value back make sure this is the VM that the vCenter Server VM  is supposed to be not some other  VM that is still present in the Inventory but powered off.

If you added the vCenter Server using the FQDN instead of the IP you use the FindByDNSName function instead.

If the VM cannot be found the MOR value will report back as VOID.

Regards,

B

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:47 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:47 PM

Hi,

My vCenter server is no VCSA, it’s a virtual machine running 2012R2. Its name is mp-vc55.

The cluster that I’m currently using only has six virtual machines and there are no duplicate IPs.

Testing through MOR was completely OK; it found the correct vCenter server.

Please find the requested file in attachment.

Best regards,

Wouter

Attachments
VirtualizationFileStore.properties.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:46 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:46 PM

Hi,

Initial diagnosis is there is an issue with DNS. Is the domain name server running as a VM?  If it is then you need to add the VMware host info to C:\Windows\System32\drivers\etc\hosts. Another option is to add the host to vCenter using their IP addresses instead of FQDN.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:46 PM

0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:10 AM . Last Modified: ‎2024-03-04 11:46 PM

Hi Bill,

DNS is running on two DC’s, both virtual machines. One of them was indeed running on the cluster that was being shut down!

I entered the VMware hosts’ IPs into the hosts file on the PCNS server and now the shutdown sequence seems OK!

Now all I have to do is change the ”on battery” event to a “battery remaining” and test the startup procedure as well.

Thanks for your help!

Best regards,

Wouter

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore