PCNS 3.0.0 Security information is incorrect

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS 3.0.0 Security information is incorrect
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

0 Likes
10
1654
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

PCNS 3.0.0 Security information is incorrect

Hello,

we have 4 vSphere ESXi 4.1 server and 4 APC Smart UPS 1500.
In each server operates one vMA 4.1. In each vMA PCNS 3.0.0 was installed.

We configured PCNS with internet explorer 8. The username, password and the authentication phrase is all UPS the same.
Unfortunately, the configuration works only on a UPS.

On the other 3 UPS we get the error:
"ERROR: NMC http://192.168.1.174:80 found incorrect, but is information security. Check the User Name and Authentication Phrase."

A firmware update and reboot the AP9617 has been carried out.

Request for support:)
Tom

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
frank_at_nilzen.net_apc
Crewman frank_at_nilzen.net_apc
Crewman

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:54 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:54 PM

Hi.

I tried a reset one more time and now it seems to work πŸ™‚
Thanks.

/frank

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

Glad to hear that you got it up and running. Congratulations.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

No, I could solve the problem:
The authentication phrase must have a certain number of characters.
"test123" was too short. With a longer phrase is working πŸ™‚

Thank you for your time Jon !!!

Message was edited by: TomOnline

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

Hi Tom,

First I would like to know how was PCNS installed on each ESXi, is it Single UPS, Redundant or Parallel?

Next, did the PCNS and NMC do have the same username? This is one of the requirement when installing PCNS also did you change or key in a different authentication phrase? The default authentication phrase for the NMC is admin user phrase, try changing this on each NMC and use this when installing PCNS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

Hello Jon,

1) It is a single UPS (hc_1314.jpg).

2) NMC and PCNS have the same username and password (hc_1315.jpg).

3) Today a change the Authentication Phrase to the same password like PCNS and NMC (hc_1316.jpg).

Please help.
Tom

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:14 AM . Last Modified: β€Ž2024-03-10 11:55 PM

Problem solved πŸ™‚ => hc_1317.jpg

Did you know my problem ?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:55 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:55 PM

TomOnline,

After changing and applying those things that you did on your previous post, did it work right away or you had to wait for sometime? The most common things why this would cause a problem is a totally different authentication phrase. The NMC and PCNS do have different phrases configured on them.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:55 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:55 PM

I totally forgot about the length of the authentication phrase. The acceptable length is 15 to 32 ASCII characters.

Reply

Link copied. Please paste this link to share this article on your social media post.

frank_at_nilzen.net_apc
Crewman frank_at_nilzen.net_apc
Crewman

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:54 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:54 PM

Hi.

I have the exact same problem, but I dont think it is the lenght of the authentication phrase that is wrong.

I have single Smart UPS 1500 with MGMT card AP 9631 and 7-8 servers (windows, linux and ESX)

I'm new to this, so i may be doing something wrong πŸ™‚

I have updated to newest firmware and restarted the UPS/Card and connected the servers to the UPS and now when I try to install PCNS 3.0.0 (on windows server 2008 R2 x64) it gives me the error msg:
"ERROR: NMC http://ip address:80 found incorrect, but is information security. Check the User Name and Authentication Phrase."

I have tried different aut. phrases, and tried to set it to standard (admin user phrase), but I still got the error.

I am also not sure where I set the auth. phrase, there is more than one place to set it. Anyone know the difference?

1. UPS - Configuration - shutdown - authentication phrase
2. UPS - Configuration - sync control - authentication phrase (and encryption phrase)

I have set the phase to the same both places.

I'm logging in to the webGUI with the default "administrator" user and have set the password in (administration - security - local users)
And i'm using the same login at the client.


Any idea anyone????

Thanks in advance πŸ™‚

Message was edited by: frank@nilzen.net

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:54 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:54 PM

Hi Frank,

The authentication phrase that PCNS looks for should be set up on UPS>Configuration>Shutdown>Authentication Phrase.

On all servers/computers that you've been using, they all do not work or communicated with PCNS? Can you do a Reset to Defaults Except TCP/IP on the network management card and try the PCNS Configuration Wizard one more time?

Reply

Link copied. Please paste this link to share this article on your social media post.

frank_at_nilzen.net_apc
Crewman frank_at_nilzen.net_apc
Crewman

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:54 PM

0 Likes
0
1653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:15 AM . Last Modified: β€Ž2024-03-10 11:54 PM

Hi.

I tried a reset one more time and now it seems to work πŸ™‚
Thanks.

/frank

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of