PCBE shutdown - time required for shutdown vs battery thresholds vs runtime

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCBE shutdown - time required for shutdown vs battery thresholds vs runtime
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:01 PM . Last Modified: ‎2024-03-07 02:12 AM

0 Likes
1
2252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:01 PM . Last Modified: ‎2024-03-07 02:12 AM

PCBE shutdown - time required for shutdown vs battery thresholds vs runtime

I am a bit confused about the shutdown options in PCBE. The server this UPS is protecting is SBS 2008 and takes about 10mins to shutdown, and 15mins to startup.
I simply want in the event of power cut to run the server for 5mins, and if the power does not come back to start the shutdown, wait 10m cut power to the server, when power is restored, charge battery to 30% then restore power to server.
Perhaps someone could explain the time required for shutdown sequence actually works in the real world please?
This is what is not clear:
Time Required For Shutdown Sequence 20 Minutes
The amount of time, as entered by the user, required to complete the shutdown sequence
From the help file:
Use the UPS On Battery Thresholds to set the Runtime Remaining Threshold for your UPS. This is the threshold at which PowerChute Business Edition initiates an OS shutdown. The range is from 2 to 59 minutes. For example, if you set the the Runtime Remaining Threshold to 10 minutes, and your UPS switches to battery operation, an OS shutdown begins when your UPS's battery has only 10 minutes of runtime remaining.
Settings:
Time Required For Shutdown Sequence 20 Minutes
The amount of time, as entered by the user, required to complete the shutdown sequence.

Low Battery Signal 2 Minutes
When this signal occurs, an immediate shutdown will begin.

Command File Enabled No
Indicates if a user-configured command file will run during the shutdown sequence.

OS Shutdown Delay 10:30 Minutes:Seconds
The maximum time required for OS shutdown after the configured command file has completed. After this delay, the UPS will turn off its output, turning off power to the protected system.

OS Shutdown Type Shutdown
Allows for system shutdown, or hibernate (if supported by operating system).

Enable OS Reboot Yes
Indicates if system will start after input line power has returned.

UPS Turn On Battery Capacity 30 %
The UPS will restart once its batteries charge to at least this level.

UPS Turn On Delay 1 Minutes
The amount of time that the UPS will wait after it reaches its Turn On Battery Capacity, before returning power to the system.

Enable SMTP E-mail No
Indicates if receipt of E-mail has been enabled for shutdown.

Enable Notification No
Indicates if notification has been enabled for shutdown, which users will be notified and the rate at which notification will be repeated, if repeat notification is enabled.

Enable Logging Yes
Indicates if logging has been enabled for shutdown.

Message was edited by: Hypertronics

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:02 PM . Last Modified: ‎2024-03-07 02:12 AM

0 Likes
0
2249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:02 PM . Last Modified: ‎2024-03-07 02:12 AM

First, make sure you have the latest version of PCBE for your UPS, since the terms may vary between versions. What UPS do you have and what version of the software?

Second, based on your requirements, it sounds like you will want to use the "Time On Battery Threshold Exceeded" event to shutdown your server. This way, you can tell the UPS to initiate a graceful shutdown for your server after it has been on battery for x minutes/seconds.

You'll then want to change the runtime remaining threshold to 10m, since that's how long it takes to shutdown. In that case, with these 2 settings configured, the UPS will either run your server for 5m & initiate a shutdown or wait until there's 10m runtime remaining & initiate a shutdown, whichever comes first. Either way, the UPS will wait 10m after triggering the graceful shutdown before it cuts power.

As for your last requirement, there's a "Power Return Settings" section under Protected System > Shutdown Settings where you can require the battery to recharge to 30% prior to the UPS powering back on.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:02 PM . Last Modified: ‎2024-03-07 02:12 AM

0 Likes
0
2250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:02 PM . Last Modified: ‎2024-03-07 02:12 AM

First, make sure you have the latest version of PCBE for your UPS, since the terms may vary between versions. What UPS do you have and what version of the software?

Second, based on your requirements, it sounds like you will want to use the "Time On Battery Threshold Exceeded" event to shutdown your server. This way, you can tell the UPS to initiate a graceful shutdown for your server after it has been on battery for x minutes/seconds.

You'll then want to change the runtime remaining threshold to 10m, since that's how long it takes to shutdown. In that case, with these 2 settings configured, the UPS will either run your server for 5m & initiate a shutdown or wait until there's 10m runtime remaining & initiate a shutdown, whichever comes first. Either way, the UPS will wait 10m after triggering the graceful shutdown before it cuts power.

As for your last requirement, there's a "Power Return Settings" section under Protected System > Shutdown Settings where you can require the battery to recharge to 30% prior to the UPS powering back on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of