PCBE email notification fails.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCBE email notification fails.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

0 Likes
6
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

PCBE email notification fails.

I am trying to test notifications.
I'm using myself as sender and it works fine to my email address.
But I am also trying to send to my cell phone. This one causes a fail. I know it works because I can send myself email from my outlook to the cell phone.
Is there any log files or anything that gives more description on the failure

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:07 AM . Last Modified: ‎2024-03-07 11:29 PM

0 Likes
0
1060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:07 AM . Last Modified: ‎2024-03-07 11:29 PM

I am trying to test notifications.
I'm using myself as sender and it works fine to my email address.
But I am also trying to send to my cell phone. This one causes a fail. I know it works because I can send myself email from my outlook to the cell phone.
Is there any log files or anything that gives more description on the failure

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

0 Likes
0
1060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

Ron,

Unfortunately USB is Smart-Signaling, and therefore the circuitry hasn't been designed, nor is there an intention to that I'm aware of. The serial ports are simple signaling, and therefore, it would be basically impossible to have simple signaling USB ports due to their communication.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

Hello again K.

What I have figured out so far is, It will send to my internal email, no problem, but nothing external. I've tried both my cell phone and an email that resides elsewhere and they both fail. I've gone through the document you linked to and all that checks out

Instead of starting a new thread maybe you can answer one more quickie.
Is there a USB version of the interface expander? AP9207. I can't seem to find any.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

Hi K,
a question about your smart signalling comment.
I want to order the interface expander, and there is a choice of cables, some smart signalling and some simple. what is the difference between parts 940-0020, 940-0024, AP9804?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:06 AM . Last Modified: ‎2024-03-07 11:29 PM

Ron,

The only interface expanders available are the two port simple signaling (uses the 940-0020) (part number AP9607), and the Share-UPS interface expander (uses 1 940-0024 and 7 940-0020)(part number AP9207). Other than that, there are no additional serial interfaces that are still supported.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 07:07 AM . Last Modified: ‎2024-03-07 11:29 PM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:07 AM . Last Modified: ‎2024-03-07 11:29 PM

To debug the email notification problem, I would use wireshark to capture the traffic and see what's happening. For example, if you see it attempting to connect to an external mail server but failing, then perhaps the port is blocked. If you see it connect to your mail server but the mail server refuses to deliver, you'll find out why. One possibility is that your mail server will not relay to external addresses without authenticating to prevent misuse by spammers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:07 AM . Last Modified: ‎2024-03-07 11:29 PM

0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:07 AM . Last Modified: ‎2024-03-07 11:29 PM

I am trying to test notifications.
I'm using myself as sender and it works fine to my email address.
But I am also trying to send to my cell phone. This one causes a fail. I know it works because I can send myself email from my outlook to the cell phone.
Is there any log files or anything that gives more description on the failure

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore