Posted: 2021-06-30 02:31 AM . Last Modified: 2024-03-10 11:19 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:31 AM . Last Modified: 2024-03-10 11:19 PM
Two brand new UPS's, attempting to configure for the first time. From the web interface, I selected/applied UPS\Control\Turn On UPS Outlet Groups\Apply.
The Logs tab shows: "UPS: The output power is now turned on." and right after that entry the log shows: "UPS: The output power is turned off."
I have also tried going to UPS\Outlet Groups\control\On Immediately. With the same result.
This is my first time attempting to configure one of these, so hopefully there is some glaringly obvious thing that I'm not doing that someone can point out.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:32 AM . Last Modified: 2024-03-10 11:19 PM
can you try to turn it on via the LCD screen? i don't have one in front of me but does this have more than one outlet group? it may require you to turn them on in a certain order but i did not think that was by default? (main before secondary or something like that with delays..)
can you post the event.txt and data.txt from the NMC using these instructions? http://nam-en.apc.com/app/answers/detail/a_id/9321
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:32 AM . Last Modified: 2024-03-10 11:19 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:32 AM . Last Modified: 2024-03-10 11:19 PM
We have a winner!
I turned the outlet on from the front panel. that solved all of my issues!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:32 AM . Last Modified: 2024-03-10 11:19 PM
can you try to turn it on via the LCD screen? i don't have one in front of me but does this have more than one outlet group? it may require you to turn them on in a certain order but i did not think that was by default? (main before secondary or something like that with delays..)
can you post the event.txt and data.txt from the NMC using these instructions? http://nam-en.apc.com/app/answers/detail/a_id/9321
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:32 AM . Last Modified: 2024-03-10 11:19 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:32 AM . Last Modified: 2024-03-10 11:19 PM
We have a winner!
I turned the outlet on from the front panel. that solved all of my issues!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:32 AM . Last Modified: 2024-03-10 11:19 PM
🙂
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.