OID for front panel alarm status

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • OID for front panel alarm status
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
143
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
7
2012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

OID for front panel alarm status

It there an OID  that indicates the status of the front panel led and sound.

A Smart-UPS SRT 5000 that has a flashing led. The reason is known but i want to see it in my monitoring software.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:25 AM . Last Modified: ‎2024-02-20 04:46 AM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:25 AM . Last Modified: ‎2024-02-20 04:46 AM

Hi,

The menu options for the SRT5KXLI are listed in the installation guide on page 20

http://www.apc.com/salestools/JGNY-97QESM/JGNY-97QESM_R4_EN.pdf

nPJG3R57ZKAriVf0HztHlw%3D%3D.pngnPJG3R57ZKAriVf0HztHlw%3D%3D.png

So for example load is listed under upsAdvOutputLoad oid: 1.3.6.1.4.1.318.1.1.1.4.2.3.0 Battery charge is upsAdvBatteryCapacity oid: 1.3.6.1.4.1.318.1.1.1.2.2.1

I use PowerSNMP free manager to review OIDs You can use that software to review the OIDs you want to see and add them to your management system. 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

Hi,

Do you have a network management card installed in the SRT? If so you can use the PowerNet MIB to walk the device to see the available OIDs. The latest PowerNet MIB can be downloaded here http://www.apc.com/us/en/tools/download/download.cfm?sw_sku=SFPMIB423&software_id=MFOI-APKTJ4&family...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

Yes I have a network card an I tested a great many of OID's but did not find any for the panel.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

Hi,

What is the exact model number of the UPS? You will find that information on the bar code sticker

C3VG1R4NtREhI4Nv5HVagA%3D%3D.pngC3VG1R4NtREhI4Nv5HVagA%3D%3D.png

Depending on the model the sticker is on the front behind the bezel or on the back. If you cannot access the sticker a photo of the front of the unit will do.

LED flash based on an event and most of not all events have OID assigned to them. Flashing LEDs do not trigger an event. An event will trigger flashing LEDs the same way an event will trigger a SNMP trap. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

srt192rmbp

7s1633l01293

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

Hi,

I am sorry but that is the part number for a battery pack not a UPS. Are you asking for OID for a battery pack? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:25 AM . Last Modified: ‎2024-02-20 04:46 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:25 AM . Last Modified: ‎2024-02-20 04:46 AM

sorry I should have known

SRT5KXLI
AS 1636271839

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:25 AM . Last Modified: ‎2024-02-20 04:46 AM

0 Likes
0
2014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:25 AM . Last Modified: ‎2024-02-20 04:46 AM

Hi,

The menu options for the SRT5KXLI are listed in the installation guide on page 20

http://www.apc.com/salestools/JGNY-97QESM/JGNY-97QESM_R4_EN.pdf

nPJG3R57ZKAriVf0HztHlw%3D%3D.pngnPJG3R57ZKAriVf0HztHlw%3D%3D.png

So for example load is listed under upsAdvOutputLoad oid: 1.3.6.1.4.1.318.1.1.1.4.2.3.0 Battery charge is upsAdvBatteryCapacity oid: 1.3.6.1.4.1.318.1.1.1.2.2.1

I use PowerSNMP free manager to review OIDs You can use that software to review the OIDs you want to see and add them to your management system. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore