Posted: 2021-07-08 02:24 AM
This question was originally posted by Gregor on APC forums on 7/27/2017
It there an OID that indicates the status of the front panel led and sound.
A Smart-UPS SRT 5000 that has a flashing led. The reason is known but i want to see it in my monitoring software.
Posted: 2021-07-08 02:25 AM
This reply was originally posted by Bill on APC forums on 8/2/2017
Hi,
The menu options for the SRT5KXLI are listed in the installation guide on page 20
http://www.apc.com/salestools/JGNY-97QESM/JGNY-97QESM_R4_EN.pdf
So for example load is listed under upsAdvOutputLoad oid: 1.3.6.1.4.1.318.1.1.1.4.2.3.0 Battery charge is upsAdvBatteryCapacity oid: 1.3.6.1.4.1.318.1.1.1.2.2.1
I use PowerSNMP free manager to review OIDs You can use that software to review the OIDs you want to see and add them to your management system.
Posted: 2021-07-08 02:24 AM
This reply was originally posted by Bill on APC forums on 7/31/2017
Hi,
Do you have a network management card installed in the SRT? If so you can use the PowerNet MIB to walk the device to see the available OIDs. The latest PowerNet MIB can be downloaded here http://www.apc.com/us/en/tools/download/download.cfm?sw_sku=SFPMIB423&software_id=MFOI-APKTJ4&family...
Posted: 2021-07-08 02:24 AM
This reply was originally posted by Gregor on APC forums on 8/1/2017
Yes I have a network card an I tested a great many of OID's but did not find any for the panel.
Posted: 2021-07-08 02:24 AM
This reply was originally posted by Bill on APC forums on 8/1/2017
Hi,
What is the exact model number of the UPS? You will find that information on the bar code sticker
Depending on the model the sticker is on the front behind the bezel or on the back. If you cannot access the sticker a photo of the front of the unit will do.
LED flash based on an event and most of not all events have OID assigned to them. Flashing LEDs do not trigger an event. An event will trigger flashing LEDs the same way an event will trigger a SNMP trap.
Posted: 2021-07-08 02:24 AM
This reply was originally posted by Gregor on APC forums on 8/2/2017
srt192rmbp
7s1633l01293
Posted: 2021-07-08 02:24 AM
This reply was originally posted by Bill on APC forums on 8/2/2017
Hi,
I am sorry but that is the part number for a battery pack not a UPS. Are you asking for OID for a battery pack?
Posted: 2021-07-08 02:25 AM
This reply was originally posted by Gregor on APC forums on 8/2/2017
sorry I should have known
SRT5KXLI
AS 1636271839
Posted: 2021-07-08 02:25 AM
This reply was originally posted by Bill on APC forums on 8/2/2017
Hi,
The menu options for the SRT5KXLI are listed in the installation guide on page 20
http://www.apc.com/salestools/JGNY-97QESM/JGNY-97QESM_R4_EN.pdf
So for example load is listed under upsAdvOutputLoad oid: 1.3.6.1.4.1.318.1.1.1.4.2.3.0 Battery charge is upsAdvBatteryCapacity oid: 1.3.6.1.4.1.318.1.1.1.2.2.1
I use PowerSNMP free manager to review OIDs You can use that software to review the OIDs you want to see and add them to your management system.