Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

OID for front panel alarm status

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: OID for front panel alarm status
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM

0 Likes
7
450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 02:24 AM

OID for front panel alarm status

This question was originally posted by Gregor on APC forums on 7/27/2017


It there an OID  that indicates the status of the front panel led and sound.

A Smart-UPS SRT 5000 that has a flashing led. The reason is known but i want to see it in my monitoring software.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:25 AM

0 Likes
0
451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 02:25 AM

This reply was originally posted by Bill on APC forums on 8/2/2017


Hi,

The menu options for the SRT5KXLI are listed in the installation guide on page 20

http://www.apc.com/salestools/JGNY-97QESM/JGNY-97QESM_R4_EN.pdf

So for example load is listed under upsAdvOutputLoad oid: 1.3.6.1.4.1.318.1.1.1.4.2.3.0 Battery charge is upsAdvBatteryCapacity oid: 1.3.6.1.4.1.318.1.1.1.2.2.1

I use PowerSNMP free manager to review OIDs You can use that software to review the OIDs you want to see and add them to your management system. 

See Answer In Context

Attachments
Reply
Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM

0 Likes
0
451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 02:24 AM

This reply was originally posted by Bill on APC forums on 7/31/2017


Hi,

Do you have a network management card installed in the SRT? If so you can use the PowerNet MIB to walk the device to see the available OIDs. The latest PowerNet MIB can be downloaded here http://www.apc.com/us/en/tools/download/download.cfm?sw_sku=SFPMIB423&software_id=MFOI-APKTJ4&family...

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM

0 Likes
0
451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 02:24 AM

This reply was originally posted by Gregor on APC forums on 8/1/2017


Yes I have a network card an I tested a great many of OID's but did not find any for the panel.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM

0 Likes
0
451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 02:24 AM

This reply was originally posted by Bill on APC forums on 8/1/2017


Hi,

What is the exact model number of the UPS? You will find that information on the bar code sticker

Depending on the model the sticker is on the front behind the bezel or on the back. If you cannot access the sticker a photo of the front of the unit will do.

LED flash based on an event and most of not all events have OID assigned to them. Flashing LEDs do not trigger an event. An event will trigger flashing LEDs the same way an event will trigger a SNMP trap. 

Attachments
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM

0 Likes
0
449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 02:24 AM

This reply was originally posted by Gregor on APC forums on 8/2/2017


srt192rmbp

7s1633l01293

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM

0 Likes
0
449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 02:24 AM

This reply was originally posted by Bill on APC forums on 8/2/2017


Hi,

I am sorry but that is the part number for a battery pack not a UPS. Are you asking for OID for a battery pack? 

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:25 AM

0 Likes
0
449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 02:25 AM

This reply was originally posted by Gregor on APC forums on 8/2/2017


sorry I should have known

SRT5KXLI
AS 1636271839

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:25 AM

0 Likes
0
452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 02:25 AM

This reply was originally posted by Bill on APC forums on 8/2/2017


Hi,

The menu options for the SRT5KXLI are listed in the installation guide on page 20

http://www.apc.com/salestools/JGNY-97QESM/JGNY-97QESM_R4_EN.pdf

So for example load is listed under upsAdvOutputLoad oid: 1.3.6.1.4.1.318.1.1.1.4.2.3.0 Battery charge is upsAdvBatteryCapacity oid: 1.3.6.1.4.1.318.1.1.1.2.2.1

I use PowerSNMP free manager to review OIDs You can use that software to review the OIDs you want to see and add them to your management system. 

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc