Not expected Firmware installed at switchgear board PX 250/500

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Not expected Firmware installed at switchgear board PX 250/500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
raheem69_apc
Ensign raheem69_apc
Ensign

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-02-14 02:32 AM

0 Likes
4
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-02-14 02:32 AM

Not expected Firmware installed at switchgear board PX 250/500

Dear All,

The below mentioned warning alarm appears on Symmetra PX 250/500.

" not expected firmware installed at switchgear board" .

The fault appeared right after installation of new firmware ver 4.24.8.

Can anyone help me out.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
raheem69_apc
Ensign raheem69_apc
Ensign

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
1884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-02-14 02:22 AM

Yes we have contacted local APC technical team and complaint was logged regarding the issue.

Serial Number of our UPS is QD1113140132.

Thank you for supporting in this regard.


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-01-31 02:54 AM

0 Likes
0
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-01-31 02:54 AM

I assume an APC Field Service Engineer (FSE) came to your site and upgraded the firmware recently on the UPS?

Either way, this will require an FSE to resolve now. Seems as though one of your switchgear cards/boards/modules does not have the correct firmware on it and only certified FSEs can do this procedure unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

raheem69_apc
Ensign raheem69_apc
Ensign

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-02-14 02:32 AM

0 Likes
0
1886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-02-14 02:32 AM

Yes this is right APC Local Dealer in Pakistan has updated the firmware and from that time the above mentioned fault is appearing. The firmware in our  4x Symmetra PX500 (450kW ,N 1) was updated but only 01 out of 04  has got the above mentioned faults while the rest of three are working fine.

APC Local Partners have tried but unable to resolve the above issue.

Please advise a solution.

Message was edited by: Raheem Orangzeb

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-01-31 02:54 AM

0 Likes
0
1886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-01-31 02:54 AM

Have you tried to contact your local APC technical support to escalate? Do you have any case numbers I can reference to try and escalate it? If not, I'll have you message me one of your serial numbers and maybe I can look it up that way.

Reply

Link copied. Please paste this link to share this article on your social media post.

raheem69_apc
Ensign raheem69_apc
Ensign

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:41 PM . Last Modified: ‎2024-02-14 02:22 AM

Yes we have contacted local APC technical team and complaint was logged regarding the issue.

Serial Number of our UPS is QD1113140132.

Thank you for supporting in this regard.


Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore