APC Silcon SL60KH ECO mode using more power than normal

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Silcon SL60KH ECO mode using more power than normal
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
jddixon_apc
Crewman jddixon_apc
Crewman

Posted: ‎2021-07-29 09:31 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
2
929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:31 PM . Last Modified: ‎2024-02-14 02:22 AM

APC Silcon SL60KH ECO mode using more power than normal

Hi Everyone

We have a APC Silcon SL60KH that seams to pull 3-4x MORE power when eco-mode is active than when normal operation is selected. In Eco-mode the inverter is off and it pulls around 18amps per phase. When in normal mode the inverter is on and it pulls 3-4amps per phase (the room also gets pretty warm. Has anyone else witnessed this behaviour and any idea what could be the problem? The data floor it is serving is empty at the moment (no load) but when we attached a 1200w load the same range of readouts were observed. Also when eco-mode is active the menu on the front of the unit indicates it is pulling 1 amp per phase when the facility meter indicates substantially more.

The UPS itself is quite old and is of 3phase 415v design. It had a new PSU board not so long ago as some of the small capacitors were swollen. 

Any advice would be grateful.

Thanks

Jon Dixon

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jddixon_apc
Crewman jddixon_apc
Crewman

Posted: ‎2021-07-29 09:31 PM . Last Modified: ‎2024-02-14 02:32 AM

0 Likes
0
930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:31 PM . Last Modified: ‎2024-02-14 02:32 AM

Hi Bill

Thanks for replying. We decided to retire the unit in the end and replace it with 2 more modern Smart UPS VT units.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:31 PM . Last Modified: ‎2024-01-31 02:54 AM

0 Likes
0
929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:31 PM . Last Modified: ‎2024-01-31 02:54 AM

Hi,

While in ECO mode the UPS would be running on the Static Switch - essentially connecting the loads directly to the input. You would never expect to see more current in ECO mode then when in normal. While in ECO mode there is no input power factor correction, but as you mentioned there is no load here at all, so nothing that would be going back to utility anyway. And it is also interesting that you mention the display shows little to no current, but it is definitely pulling it as you have metered it.

So having said all that, our suspicions would be something is wrong with the static switch, or the control issues to the static switch. This is definitely a good one to call into the local tech support group for your country.

Link to local support contact page http://www.apc.com/site/support/index.cfm/contact-information/

Reply

Link copied. Please paste this link to share this article on your social media post.

jddixon_apc
Crewman jddixon_apc
Crewman

Posted: ‎2021-07-29 09:31 PM . Last Modified: ‎2024-02-14 02:32 AM

0 Likes
0
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:31 PM . Last Modified: ‎2024-02-14 02:32 AM

Hi Bill

Thanks for replying. We decided to retire the unit in the end and replace it with 2 more modern Smart UPS VT units.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore