No power output smart ups 3000 VA XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • No power output smart ups 3000 VA XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
10
4206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

No power output smart ups 3000 VA XL

      Hi all,

I have inherited a smart ups 3000 VA XL.  Everything seems OK.. batteries are at 100%. Fans come on.  Pull plug out and the batteries kick in.  Self Test in PowerChute claims to be OK. 

However, I cant power anything through the power out sockets on the back.. not even a monitor.  Powerchute shows that the load is always 0.0%

Am I missing a Magic button or switch? Is there a hidden output circuit breaker?

Any ideas / suggestions?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:51 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:51 PM . Last Modified: ‎2024-03-11 04:27 AM

Hi Ajbird,

Couple of last things you could do / try before having it serviced are:

1. With the side/cover off did you check to see that the white molex connectors feeding power from the main UPS circuit board to the rear panel receptacles are all 100 % tight and not coming loose ? (make sure uPS is powered off / unplugged and discharged for safety when poking at them( press power button with ups and battery unplugged or wait a day or two with ups off and battery disconnected ).

I have seen cases where these internal connectors have come lose due to the UPS being banged or jostled during handling or shipping. Can happen within battery modules as well.

2. Do you have one of those plug in three-prong outlet testers ? These have lamps/leds to tell you whether the power coming from the back panel receptacles is "complete", IE no missing grounds, missing neutrals, hot to neutral or ground to neutral mixups.

Good luck!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

If a self test happens, it should be running online. This unit probably will have an input breaker near the power plug on it but if the UPS is online, it should be outputting power.

Can you tell us the exact UPS model from the white sticker on the back of the UPS please? Can you give us any screenshots of PowerChute indicating the status of the UPS? it should say online, on battery, output off, etc some place. An event log from PowerChute may be helpful too to better understand the state of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

Hi

Model : SUA3000XLI

Images:

1059_ups1.PNG

1060_ups2.PNG

1061_ups3.PNG

1062_ups4.PNG

Powerchute:

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

ok - great. thank you. This is a big help. The UPS believes it is online and running properly. The rear of your UPS looks like this, correct? http://www.apc.com/products/moreimages.cfm?partnum=SUA3000XLI it seems like the breaker next to the input plug would not be the problem because that is the input breaker. it also appears the actual receptacles have no circuit breakers.

did you try multiple pieces of equipment connected? is it possible to measure the AC voltage with a voltmeter on all of the receptacles? the UPS things its outputting voltage properly so we'll have to confirm that with the items I just asked or suggested.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

HI (really appreciate your help)

Yes, that is the back of the UPS

I have tried a very low power NAS / several monitors.  I am sure there is no power leaving the rear of the device.

Is there a fuse or anything I cant see?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

hmm very strange. no fuse - did this UPS ever work? i imagine so, or is it brand new?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

I also have a by pass panel.. using the large  -socket output to connect to the panel also seems to indicate that this is also dead (as well as the 8 sockets)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

yes, that makes sense. the only thing I would do if it were me is just really verify that the bypass panel is in normal mode vs. test or maintenance but if it was, then you should have power at the bypass panel sockets anyway..i guess unless it was wired wrong.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

OK i have taken the side panel off and can see that all the power out sockets 8 + 1 go straight back to the motherboard. grr

Can these things be repaired  in the UK?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

I am not sure - UK tech support may know better. I only know of the repair facilities in the USA.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:51 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
4202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:51 PM . Last Modified: ‎2024-03-11 04:27 AM

Hi Ajbird,

Couple of last things you could do / try before having it serviced are:

1. With the side/cover off did you check to see that the white molex connectors feeding power from the main UPS circuit board to the rear panel receptacles are all 100 % tight and not coming loose ? (make sure uPS is powered off / unplugged and discharged for safety when poking at them( press power button with ups and battery unplugged or wait a day or two with ups off and battery disconnected ).

I have seen cases where these internal connectors have come lose due to the UPS being banged or jostled during handling or shipping. Can happen within battery modules as well.

2. Do you have one of those plug in three-prong outlet testers ? These have lamps/leds to tell you whether the power coming from the back panel receptacles is "complete", IE no missing grounds, missing neutrals, hot to neutral or ground to neutral mixups.

Good luck!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of