Planned 12 Hour Power Outage: What to do.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Planned 12 Hour Power Outage: What to do.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
3
910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

Planned 12 Hour Power Outage: What to do.

Hi All,

We have a Symmetra RM 6000 that all our servers are on. We are having a planned outage by our power company of 12 hours overnight and wondering what the best thing to do is. I plan on shutting all our servers down and powering off, so they will be very little pulling power from the UPS, but I was wondering if it was best to leave the UPS on, put in bypass, or shut it off.

Or does it make a difference

Many Thanks,

CWH

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

After you power your servers down and nothing else is relying on output from the UPS, go ahead and turn off the System Enable switch on the front of the UPS. You'll need to take the bezel off and you'll see this switch right near the intelligence modules on the right hand side behind that bezel. Then, just dis-engage the batteries as I noted. To turn back on, insert the batteries first and make sure they are fully seated and then turn system enable on. To have the output turned on once the UPS electronics turn back on, you'll need to use either the front powerview display or management card to turn the UPS output on. If in the NMC, you'll see it under Control most likely and then on the front powerview display, it is under the control menu too.

here is the operator's guide for reference: http://www.apcmedia.com/salestools/ASTE-6Z3QGM/ASTE-6Z3QGM_R2_EN.pdf

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

Hi claytonh - We'd suggest you power down the UPS completely and then dis-engage any battery modules. If you have any extended run frames, don't forget to dis-engage the batteries on those as well. To dis-engage, just slide them out a few inches so they are not connected to the frame.

During any extended (let's say more then 2 hours) power down or storage of the UPS, if you leave them connected, they will discharge into the UPS and you'll have dead batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

Let me ask a stupid question then. How do I power it down? Is it the Input Circuit Breaker in the back or is it something through the software interface?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

0 Likes
0
910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:50 PM . Last Modified: ‎2024-03-11 04:27 AM

After you power your servers down and nothing else is relying on output from the UPS, go ahead and turn off the System Enable switch on the front of the UPS. You'll need to take the bezel off and you'll see this switch right near the intelligence modules on the right hand side behind that bezel. Then, just dis-engage the batteries as I noted. To turn back on, insert the batteries first and make sure they are fully seated and then turn system enable on. To have the output turned on once the UPS electronics turn back on, you'll need to use either the front powerview display or management card to turn the UPS output on. If in the NMC, you'll see it under Control most likely and then on the front powerview display, it is under the control menu too.

here is the operator's guide for reference: http://www.apcmedia.com/salestools/ASTE-6Z3QGM/ASTE-6Z3QGM_R2_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of