Hello Everyone,
I did a search for "No UPS Found" and found several issues resolved with either reloading the firmware, rebooting or selecting the wrong firmware. None of those seem to apply here.
I have a Smart UPS that I believe is configured properly with the proper firmware. I was attempting initial configuration of the card that was never setup previously and noticed the "No UPS Found error" I used Datacenter Expert to select and upgrade the software as I have with a few other UPSes successfully. from v6.x to v7.0.4 as below. The "No UPS Found" error still persists.
Anyone have some advice here?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-03-10 01:29 PM
I suggest you manually flash the firmware. See Schneider Electric FAQ http://www.apc.com/us/en/faqs/FA156047