No Data Logging on SMX1500RM2U Running PCBE 9.0 with Smart Signaling

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • No Data Logging on SMX1500RM2U Running PCBE 9.0 with Smart Signaling
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:18 PM . Last Modified: ‎2024-03-06 03:20 AM

0 Likes
2
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:18 PM . Last Modified: ‎2024-03-06 03:20 AM

No Data Logging on SMX1500RM2U Running PCBE 9.0 with Smart Signaling

Data Log is enabled with a 10 minute interval, but is empty. Refresh is grayed out and inactive.

Event Log is also enabled and logs events correctly with usable Refresh.

Log access is via PCBE console. PCBE Product Update says software is up-to-date.

Host is running Vista Ultimate SP2 and is connected using USB cable provided with SMX1500RM2U.

I know that data logging is not available with Simple-Signaling, but Signaling Status shows Smart Signaling and connection is USB.

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:18 PM . Last Modified: ‎2024-03-06 03:20 AM

0 Likes
0
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:18 PM . Last Modified: ‎2024-03-06 03:20 AM

No problems in either the Windows Application or System event logs, but I did some experimentation...

(1) Copied the EventLog file (thereby duplicating ACLs and ruling out a permissions problem), emptied it and renamed it DataLog. After restarting the Agent service, it locked the file (as verified by NirSoft's OpenedFilesView), but wrote nothing to it.

(2) Restored a backup copy of DataLog generated by PCBE 7.0.5 (which was used with the SUA1500 that the SMX1500RM2U replaced). After restarting the Agent service, it truncated the file, removing the old data and leaving only the first line of the file containing the column headings for the various parameters, but again, no data was logged.

From the front panel LCD:
UPS Firmware 1: UPS 03.6
UPS Firmware 2: COM 03.6
UPS Firmware 3: UBL 05.0
UPS Firmware 4: CBL 02.1

PCBE 9.0 Build 613 with Agent 9.0.0.13

I hate to ask this, but after my experience with the S20BLK data logging problem, do you have access to a unit to confirm that an SMX1500RM2U with the given firmware and software actually logs data?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:18 PM . Last Modified: ‎2024-03-06 03:20 AM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:18 PM . Last Modified: ‎2024-03-06 03:20 AM

If you access the PCBE console and double click the UPS to view its status, do you get valid data (e.g. input voltage, output voltage)?
Yes, everything is correct except for empty Data Log.
If you access the PCBE agent web interface instead of the PCBE console interface and browse to the data log, do you have valid values?
No, Data Log > View Log simply displays "No Data Logged". Data Log > Configure Log shows data logging is enabled and configured.
Check out the install directory on the machine with the PCBE agent portion. Go into the agent folder and look for two files: EventLog and DataLog. Are they there?
EventLog is present, but there is no DataLog. I also restarted all 3 PCBE components (Agent, Server, Console), and still nothing.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:18 PM . Last Modified: ‎2024-03-06 03:20 AM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:18 PM . Last Modified: ‎2024-03-06 03:20 AM

No problems in either the Windows Application or System event logs, but I did some experimentation...

(1) Copied the EventLog file (thereby duplicating ACLs and ruling out a permissions problem), emptied it and renamed it DataLog. After restarting the Agent service, it locked the file (as verified by NirSoft's OpenedFilesView), but wrote nothing to it.

(2) Restored a backup copy of DataLog generated by PCBE 7.0.5 (which was used with the SUA1500 that the SMX1500RM2U replaced). After restarting the Agent service, it truncated the file, removing the old data and leaving only the first line of the file containing the column headings for the various parameters, but again, no data was logged.

From the front panel LCD:
UPS Firmware 1: UPS 03.6
UPS Firmware 2: COM 03.6
UPS Firmware 3: UBL 05.0
UPS Firmware 4: CBL 02.1

PCBE 9.0 Build 613 with Agent 9.0.0.13

I hate to ask this, but after my experience with the S20BLK data logging problem, do you have access to a unit to confirm that an SMX1500RM2U with the given firmware and software actually logs data?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of