UPS Network Management Card AP9618 interval Email

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS Network Management Card AP9618 interval Email
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 11:17 PM . Last Modified: β€Ž2024-03-06 03:20 AM

0 Likes
5
3366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 11:17 PM . Last Modified: β€Ž2024-03-06 03:20 AM

UPS Network Management Card AP9618 interval Email

Hello,

I have a UPS Network Management Card AP9618 and got the email notification working in the Network Management Card. However, the email notification goes out every 4 minutes when the UPS is off and wont stop until I turn the unit back on. Is there a way to set an interval or just have the email notification go out once per event?

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

0 Likes
0
3367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

yes you might want to look into changing the setting on one as a described above and then doing a mass configuration on the event action configuration section of the config.ini file on the NMC -> http://nam-en.apc.com/app/answers/detail/a_id/8979/

ultimately, i'd suggest going through the web UI on an NMC and changing the configuration there then following the instructions to download the config.ini. all of the email notification settings for which events are emailed are under EventActionConfig - you can delete everything else out of this config.ini except the heading of EventActionConfig and what's under it then cascade this portion of the file to all of your devices. this can also be done via struxureware central if you own that.

hope that helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 11:17 PM . Last Modified: β€Ž2024-03-06 03:20 AM

0 Likes
0
3367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 11:17 PM . Last Modified: β€Ž2024-03-06 03:20 AM

yes, as long as are you at 3.x email, you can configure email events easily.

click on the Administration tab->Notification sub heading and then click on Event Actions either by Event or By Group.

from there, you can choose events by severity, by group or by individual event and change their frequency, delays, etc per recipient.

hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

0 Likes
0
3367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

Thank you much. πŸ™‚ Seems to work.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

0 Likes
0
3367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

glad to hear. just an FYI - when you enable email generation in general, the default setting is to receive ALL events from the NMC every 2 minutes, until the condition clears. APC does this to give you more notifications, rather than too little, in fear of a user missing a critical alert. to change this, a user can customize alerting to their liking, based on the instructions I provided above.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

0 Likes
0
3367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

Any way to change this default easily? We have hundreds of UPSes and clicking through the settings on each one is not an appealing idea.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

0 Likes
0
3368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 11:18 PM . Last Modified: β€Ž2024-03-06 03:20 AM

yes you might want to look into changing the setting on one as a described above and then doing a mass configuration on the event action configuration section of the config.ini file on the NMC -> http://nam-en.apc.com/app/answers/detail/a_id/8979/

ultimately, i'd suggest going through the web UI on an NMC and changing the configuration there then following the instructions to download the config.ini. all of the email notification settings for which events are emailed are under EventActionConfig - you can delete everything else out of this config.ini except the heading of EventActionConfig and what's under it then cascade this portion of the file to all of your devices. this can also be done via struxureware central if you own that.

hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore