Newbie to PowerChute software on PC needs advice

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Newbie to PowerChute software on PC needs advice
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:00 AM . Last Modified: ‎2024-02-29 10:22 PM

0 Likes
5
1649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:00 AM . Last Modified: ‎2024-02-29 10:22 PM

Newbie to PowerChute software on PC needs advice

Hello all, pls forgive me if the question sounds stupid - but Im new to this with a PC.

My situation is as follows. 
In my office room in 1st floor I have a Mac Laptop and a Windows 7 laptop - plugged to a APC Back-UPS 800
Unfortunately I now have to move my QNAP TS-453A to the basement as I connect it to my TV - and the 20m HDMI cable doesnt support me with sound. 😞

So now I need the powerchute software running on my PC to signal the QNAP NAS in case of a power outage to shutdown.

My NAS has a fixed IP - so what would be the best way to do this ?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

0 Likes
0
1649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

Hi,

Read this section of the APCUPSD User's Guide NIS Server/Client Configuration Using the Net Driver for assistance with powering down 2 or more computers. 

To power down the NAS you will need to write a script. You may find information on how to remotely power down the NAS from the manufactures web site or they may have a forum or User's Group that could help. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:00 AM . Last Modified: ‎2024-02-29 10:22 PM

0 Likes
0
1649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:00 AM . Last Modified: ‎2024-02-29 10:22 PM

Hi,

We do not officially support running command files with PowerChute Personal Edition however there is a forum post that explains how to do so.

http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/14110/newbi...

If you're not comfortable scripting PowerChute Personal Edition you could try APCUPSD. APCUPSD allow for the running of command files / scripts prior to shutdown and will run on the Windows and Mac systems. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

0 Likes
0
1649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

Thanks for the info.

Maybe someone checks the APCUPSD Website from time to time as it gives only this:

Application Error

The application has experienced an error - we apologize for the inconvenience.

Our technical team was notified and is looking into the issue now.

Please try the following:

  • Return to the community homepage.
  • Click the Back button in your browser to try a different link.
  • If you typed the address in the Address Bar, make sure that it is spelled correctly.
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

0 Likes
0
1649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

Hi,

Sorry for the inconvenience. The link is broken for some reason but the site is up. Open you browser and enter apcupsd.org to access the site. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

0 Likes
0
1649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

Ok got it now and installed on my Macbook. Good thing is I now have a small monitor for the UPS.

But is there any information on how to setup this thing?
I mean all I need is to signal 1 Win7 Laptop and 1 QNAP NAS to shutdown on loss of power.
But in the manual I didnt really find how to do that.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM

Hi,

Read this section of the APCUPSD User's Guide NIS Server/Client Configuration Using the Net Driver for assistance with powering down 2 or more computers. 

To power down the NAS you will need to write a script. You may find information on how to remotely power down the NAS from the manufactures web site or they may have a forum or User's Group that could help. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore