Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

New Smart-UPS X 1500VA and bizarre noises...

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • New Smart-UPS X 1500VA and bizarre noises...
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:22 AM . Last Modified: β€Ž2024-03-10 11:34 PM

0 Likes
9
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:22 AM . Last Modified: β€Ž2024-03-10 11:34 PM

New Smart-UPS X 1500VA and bizarre noises...

Hi,

I just acquired a Smart-UPS X 1500VA to support two servers in a improvised rack in my home office. When both servers are up, the max. load is at most 10% as shown by the display; I know it is massive overkill but I am planning a few more machines... Ok, now the situation: everyone once in a while, at different moments during the day, the UPS emits noises that are quite freakish: it goes from a loud single "klak" to brief moments of intense clicking noise. I shut the UPS down and up again, letting the auto diagnostic do its thing but it always tells me that everything is working a-ok.

Any ideas?

Best regards

Sylvain Foisy, Ph. D.
Bioinformatics Consultant
Diploide BioIT
Montreal,Qc

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:26 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:26 PM

Hi,

A simple progress report... Now a week with the power quality setting at Fair and no more noise πŸ˜‰ A guess: this setting males the UPS more tolerant to input power issues?

Thanks for the inpues

Sylvain

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

Hi Sylvain,

Whenever the UPS makes that sound do you see any LED that comes on? It is possible that the UPS detects power disturbances and to ensure that your load gets clean power it, it transfers over to battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

Hi,

Not sure about this: most of the time, I am not close to the UPS when th noises are emitted. I'll be paying more attention to answer your question.

Sylvain

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

might be helpful if you have a network management card or powerchute software to review it and see if there are any transfers to battery or AVR.

i was curious to know what firmware is on your UPS as well for UBL, UPS, CBL, and COM versions. you can get this via NMC/software or via the LCD menu. make sure the menu is set to advanced mode to get all of the versions i mentioned though. i think thats changed under the configuration menu and then firmware listed in About.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

Hi,

I was planning on installing apcupsd on one of the servers to monitor the UPS; I guess I'll move forward on this. As for the extra pieces of data, I'll post when I get home tonight πŸ™‚

Best regards

Sylvain

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

ok. we'll wait for the info

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

Hi,

Ok, here are the firmware versions:

UPS : 03.7
COM: 03.6
UBL : 05.0
CBL : 02.1

There has been no noise for the past ~24 hrs and apcupsd hasn't reported anything out of the ordinary... Keeping the watch πŸ™‚

Best

Sylvain

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:34 PM

There's a possibility that it is the UPS either boosting or trimming your input voltage and from time-to-time it goes to battery once it can no longer boost or trim it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:26 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:26 PM

Hi,

I went through the menu of the UPS and found that there is a setting telling it what type of power gets into the UPS in the first place. I downgraded the parameter to Fair, and ever since, no more noise... It probably doe not try to work so hard so few opportunities for cliking and clacking πŸ™‚

Best

Sylvain

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:26 PM

0 Likes
0
1115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:26 PM

Hi,

A simple progress report... Now a week with the power quality setting at Fair and no more noise πŸ˜‰ A guess: this setting males the UPS more tolerant to input power issues?

Thanks for the inpues

Sylvain

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of