ACTUAL UPS overhead (Watts) of different Smart-UPSes?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACTUAL UPS overhead (Watts) of different Smart-UPSes?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

0 Likes
6
3433
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

ACTUAL UPS overhead (Watts) of different Smart-UPSes?

I have calculated the power loss of some UPS-models from the official efficiency charts (charts are not available for all old SUA-models) and its clear that the overhead/loss in the UPS is constant over the load range. I compared the results with the specified "Online thermal dissipation" in BTU/hr (converted to W). These numbers should match, but they don't. Why?

Source of all data is for 230V models available in Sweden: [http://www.apc.com/products/family/index.cfm?id=165]

Column M is Watts directly calculated from stated BTU/hr and column N is W calculated from the efficiency charts (done in column S-AI) assuming "100% load" is 100% of the specified maximum Watts. Column P is assuming that "100% load" is max VA (which should not be possible with a resistive load).

Only SMT750RMI2U and SMT1000I are somewhat near/ok.
I have measured SUA2200RMI2U and it consumes only 40W despite a BTU/hr rating equal to 88W so perhaps the BTU/hr is overrated for a lot of models.

Message was edited by: marin849

Message was edited me: Changed topic to reflect the answer.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

0 Likes
0
3434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

I now also have a SUA750XLI and I did the same measurements on it (it also lacks an efficiency chart on the APC-website). Efficiency seems identical to SUA1000I.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

0 Likes
0
3434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

i can't say i know one way or another here what the accuracy is but a few thoughts that come to mind are:

# did you factor in online versus on battery operating modes?
# what about the battery being fully depleted and the UPS charging it with full charging power?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

0 Likes
0
3434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

1. The efficiency charts are measured during "normal operation" which I interpret as "fully charged batteries and connected to mains power". Otherwise the charts would make no sense. The BTU/hr rating (thermal dissipation during operation) is to low to be valid for the UPS thermal dissipation under full load when on batteries so I assumed that it is valid for the same condition as the efficiency chart: fully charged batteries and connected to mains input.

2. See 1. πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

0 Likes
0
3434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

I have results for the SUA1000I.
UPS overhead ranges from 16.6 W (on, no NMC, no load) to 26-30W (with NMC, full load). The rating of 100 BTU/hr is therefore correct for this unit (worst case in standby-mode with full batteries). The indicated load percentage is 8% off (0 percent is equal to 50 W, 100% is 670 W, it shows 0% up to a bit below 100W).

I still would like to know why the successor (with green technology) SMT1000I also has a rating of 100 BTU/hr (29W) while its efficiency chart gives that the overhead is 8.9 W (idle) to 9.6W (full load). My guess is that the efficiency chart is valid for full batteries and no AVR trim/boost. And that the BTU/hr rating includes AVR trim/boost being used so that the transformer is active and generating heat (SMT models can disconnect the transformer to save power - thats where the power saving comes from).

The charts are valid for SUA1000I with AP9617 installed. AP9617 adds 2.5-3.0 W.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

0 Likes
0
3434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

sorry for the delay.

I checked with one of our engineers and here is his response.

Thermal dissipation data is provided for the sole purpose of ensuring that adequate cooling is provided to the UPS. Thermal dissipation numbers are often worst case values (full load, maximum charging power, AVR transformers in use, etc.) and are not representative of typical usage conditions. Efficiency data on the other hand, is representative of steady state use and assumes nominal conditions as described in the notes which accompany the curves. If the real desire here is to compare our newest products to those that we are obsoleting, or to understand how UPS losses vary as a function of load, then the UPS Efficiency Comparison Calculator (found at http://www.apc.com/tool/?tt=5 ) should be used.

More specifically, by selecting the UPSs you want to compare, and setting the electricity cost to 0.1142, and clearing currency symbol, the electricity cost curve in the results pane becomes a loss vs. load curve as shown in the following attachment.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

0 Likes
0
3434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

Nice, then my conclusion in the previous post was correct. πŸ™‚
Thanks for the answer. That tool also looks very useable, but it doesn't have data for SUA1000I (makes sense, since there is no efficiency chart available either).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

0 Likes
0
3435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:23 AM . Last Modified: β€Ž2024-03-10 11:25 PM

I now also have a SUA750XLI and I did the same measurements on it (it also lacks an efficiency chart on the APC-website). Efficiency seems identical to SUA1000I.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore