Hello!
I have Smart UPS 3000XL with network management card 2 - AP9631
I updated the firmware network management card to 6.5 from URL:
Now I can't see menu items, responsible for managing the UPS (Shutdown, Self-Test Schedule, Scheduling, ...) in web interface of network management card (see screenshot).
What do I do?
WQm8Sh8Cx73W6qHvYpgz%2Fw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:29 PM . Last Modified: 2024-03-12 12:49 AM
Hi Oleg,
To be sure, I just downloaded the file I linked you to and it was correct:
aBejS7nOz5MyPuU82IeB6Q%3D%3D.png
I uploaded it to one of my SmartUPS and it put the proper image on (which can be found under About --> Network in the web UI):
KOsZNYI7xJjQ1NS%2FOLb%2BfQ%3D%3D.png
From your first image it shows that "sy" is currently loaded on your UPS - perhaps you have multiple firmware files saved on the machine you were pushing the upgrades from?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:28 PM . Last Modified: 2024-03-12 12:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:28 PM . Last Modified: 2024-03-12 12:50 AM
try the drop down for Control
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:28 PM . Last Modified: 2024-03-12 12:50 AM
u11V%2BmLiEXW9WYgWzsN8xg%3D%3D.png
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:28 PM . Last Modified: 2024-03-12 12:50 AM
Hi Oleg,
From your first picture, it looks like you've installed the application version "sy". This is the firmware version for Symmetra LX UPS's, and will not work with a SmartUPS. You'll need to download the "sumx" file, which you can get here: ftp://restrict:Kop$74!@ftp.apc.com/restricted/hardware/nmcard/firmware/sumx/650/apc_hw05_aos650_sumx...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:29 PM . Last Modified: 2024-03-12 12:49 AM
Hello, Matt!
see link in my first message.
link on this page same with your link
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:29 PM . Last Modified: 2024-03-12 12:49 AM
Hi Oleg,
To be sure, I just downloaded the file I linked you to and it was correct:
aBejS7nOz5MyPuU82IeB6Q%3D%3D.png
I uploaded it to one of my SmartUPS and it put the proper image on (which can be found under About --> Network in the web UI):
KOsZNYI7xJjQ1NS%2FOLb%2BfQ%3D%3D.png
From your first image it shows that "sy" is currently loaded on your UPS - perhaps you have multiple firmware files saved on the machine you were pushing the upgrades from?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:29 PM . Last Modified: 2024-03-12 12:49 AM
Matt, thank you very much!