Network Shutdown Events - How to Configure?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Network Shutdown Events - How to Configure?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
RichardParry_apc
Crewman RichardParry_apc
Crewman

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

0 Likes
2
4540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

Network Shutdown Events - How to Configure?

Hi All,

I have a single Smart UPS SRT 5000 UPS with the NMC2 card fitted, connected to a virtualised environment. I have installed PowerChute Network Shutdown for vmware and configured it with our vcenter install.

My question is, by default there are no configured Shutdown Events. I've looked everywhere online and whilst I have found tons of tutorials on how to install on Windows (non virtualised) as well as with the appliance (which we're using), there is nothing about setting up these event rules.

The shutdown settings on the UPS are as default, as is on the PCNS appliance, although I've of course configured the VM hosts in the list.

What I want the whole setup to do is stay on battery until there's about 5 minutes of battery left - at this point it will start to shutdown the VM's. The UPS has several battery expansion packs, so current runtime calibrated is about 2 hours with our fairly high load.

Can someone help please? I just need to ensure the right Shutdown Events are configured as it's not clear what needs to be done.

Thanks!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

0 Likes
0
4538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

Hi,

First, I do not recommend starting the shutdown process when the battery life is only 5 minutes. The average time for VMs to power off is 2 minutes, and the average time for PCNS and a host to power off is 3 minutes. Setting the power down at 5 minutes could cause the host not to power off cleanly. Have you tested how long it takes for the VMs to power off, and have you tested to see how long it takes for the host to power off?

Second, in your configuration, are you using vCenter Server, and if so, how many hosts are to be powered off. Do you want the VMs to automatically start up when PCNS and the host/s are back online?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

0 Likes
0
4540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

On 2/2/2021 6:56 PM, Richard said:

Hi All,

I have a single Smart UPS SRT 5000 UPS with the NMC2 card fitted, connected to a virtualised environment. I have installed PowerChute Network Shutdown for vmware and configured it with our vcenter install.

My question is, by default there are no configured Shutdown Events. I've looked everywhere online and whilst I have found tons of tutorials on how to install on Windows mypennmedicine (non virtualised) as well as with the appliance (which we're using), there is nothing about setting up these event rules.

The shutdown settings on the UPS are as default, as is on the PCNS appliance, although I've of course configured the VM hosts in the list.

What I want the whole setup to do is stay on battery until there's about 5 minutes of battery left - at this point it will start to shutdown the VM's. The UPS has several battery expansion packs, so current runtime calibrated is about 2 hours with our fairly high load.

Can someone help please? I just need to ensure the right Shutdown Events are configured as it's not clear what needs to be done.

Thanks!

 

  1. Go to Configure Events.
  2. Select UPS On Battery and click Shutdown.
  3. Click Enable Shutdown.
  4. Enter the desired amount of time you would like the UPS to run on battery prior to PowerChute starting the shutdown process and then click Apply.
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

0 Likes
0
4539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

Hi,

First, I do not recommend starting the shutdown process when the battery life is only 5 minutes. The average time for VMs to power off is 2 minutes, and the average time for PCNS and a host to power off is 3 minutes. Setting the power down at 5 minutes could cause the host not to power off cleanly. Have you tested how long it takes for the VMs to power off, and have you tested to see how long it takes for the host to power off?

Second, in your configuration, are you using vCenter Server, and if so, how many hosts are to be powered off. Do you want the VMs to automatically start up when PCNS and the host/s are back online?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore