Network Card Update show Lost Communication to the UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Network Card Update show Lost Communication to the UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:41 AM . Last Modified: ‎2024-03-08 04:11 AM

0 Likes
6
2099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:41 AM . Last Modified: ‎2024-03-08 04:11 AM

Network Card Update show Lost Communication to the UPS

I did an update on network card and after that the only information that I have is this Lost Communication to the UPS.

The UPS is SUA3000RM2U-BR and below it is the network card information.

Application Module
Name sy3p
Version v6.5.0
Date Jul 12 2017
Time 19:00:54

APC OS (AOS)
Name aos
Version v6.5.0
Date Jun 9 2017
Time 13:41:00

APC Boot Monitor
Name bootmon
Version v1.0.8
Date Apr 8 2014
Time 10:59:40

I´ve used this software to update the firmware.

lcyb42VVLHtZNeEqH1m4iw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pnglcyb42VVLHtZNeEqH1m4iw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

 

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • communication
  • lost
  • sua3000rm2u-br
  • the
  • to
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

After I rebooted the network I was able to update to the correct firmware, thanks a lot now I´ll try to update ups firmware wish me luck.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:11 AM

0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:11 AM

Please try the last firmware release. It will be the 6.8.X one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:11 AM

0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:11 AM

I´ve did the update to 6.8.0

 

Starting Upgrade 12/18/19 17:54:08
-----------------
[12/18/19 17:54:08] 10.135.30.10: Pinging (via ICMP) device
[12/18/19 17:54:08] 10.135.30.10: Device connection passed
[12/18/19 17:54:09] 10.135.30.10: Testing FTP Log-in
[12/18/19 17:54:12] 10.135.30.10: FTP Log-in passed
[12/18/19 17:54:13] 10.135.30.10: Saving data file
[12/18/19 17:54:14] 10.135.30.10: AOS Prior to firmware transfer: Network Management Card AOS v5.1.3

[12/18/19 17:54:14] 10.135.30.10: APP Prior to firmware transfer: Smart-UPS & Matrix-UPS APP v5.1.3

[12/18/19 17:54:14] 10.135.30.10: Saving event & configuration files
[12/18/19 17:54:30] 10.135.30.10: Transferring firmware file (1/3): Boot Monitor
[12/18/19 17:54:38] 10.135.30.10: Boot Monitor transfer successful
[12/18/19 17:54:40] 10.135.30.10: Restarting network interface
[12/18/19 17:55:12] 10.135.30.10: Device connection passed
[12/18/19 17:55:14] 10.135.30.10: Testing FTP Log-in
[12/18/19 17:55:14] 10.135.30.10: FTP Log-in passed
[12/18/19 17:55:15] 10.135.30.10: Transferring firmware file (2/3): OS
[12/18/19 17:56:08] 10.135.30.10: OS transfer successful
[12/18/19 17:56:10] 10.135.30.10: Restarting network interface
[12/18/19 17:56:30] 10.135.30.10: Pinging (via ICMP) device
[12/18/19 17:57:18] 10.135.30.10: Device connection passed
[12/18/19 17:57:19] 10.135.30.10: Testing FTP Log-in
[12/18/19 17:57:20] 10.135.30.10: FTP Log-in successful
[12/18/19 17:57:21] 10.135.30.10: Transferring firmware file (3/3): application
[12/18/19 17:57:59] 10.135.30.10: Restarting network interface
[12/18/19 17:58:09] 10.135.30.10: Pinging (via ICMP) device
[12/18/19 17:58:24] 10.135.30.10: No language pack selected
[12/18/19 17:58:24] 10.135.30.10: OS & Application transfer completed

But now I can´t have access on web though it still pinging.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

Hello,

The initial firmware you install was designed for a Symmetra UPS not a Smart-UPS Here is a link to the correct firmware https://www.apc.com/shop/us/en/products//P-SFSUMX680

When upgrading to firmware 6.8 once the NMC is rebooted http access is disable. To access the NMC via the web interface use https. Example https://192.168.24.100

You should read the firmware user's guide and release notes available at the link above.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

Thanks for the link and the info about https, now I can log again, i´ve tried to open release notes but link is broken.

Here is the log info when I try to install the correct firmware, this message is showed even if I enable http and ftp server.

Starting Upgrade 12/20/19 10:32:20
-----------------
[12/20/19 10:32:20] 10.135.30.10: Pinging (via ICMP) device
[12/20/19 10:32:20] 10.135.30.10: Device connection passed
[12/20/19 10:32:21] 10.135.30.10: Testing FTP Log-in
[12/20/19 10:32:26] 10.135.30.10: ERROR --> FTP Log-in failed

 

Here is the config on ssh

 

login as: apc
apc@10.135.30.10's password:

Schneider Electric Network Management Card AOS v6.8.2
(c) Copyright 2019 All Rights Reserved Symmetra APP v6.8.0
-------------------------------------------------------------------------------
Name : apc581BF6 Date : 12/20/2019
Contact : Unknown Time : 12:03:14
Location : Unknown User : Super User
Up Time : 0 Days 0 Hours 2 Minutes Stat : P+ N4+ N6+ A+
-------------------------------------------------------------------------------
IPv4 : Enabled IPv6 : Enabled
Ping Response : Enabled
-------------------------------------------------------------------------------
HTTP : Enabled HTTPS : Disabled
FTP : Enabled Telnet : Disabled
SSH/SCP : Enabled SNMPv1 : Disabled
SNMPv3 : Disabled
-------------------------------------------------------------------------------
Super User : Enabled RADIUS : Disabled
Administrator : Disabled Device User : Disabled
Read-Only User : Disabled Network-Only User : Disabled

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

0 Likes
0
2095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

Hi,

SSH to the card and enter the command ftp -S enable to enable ftp. When 6.8 is install along with disabling http access it also disable ftp access. These changes were made to bring the card into compliance with California Senate Bill No. 327

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

0 Likes
0
2098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:42 AM . Last Modified: ‎2024-03-08 04:10 AM

After I rebooted the network I was able to update to the correct firmware, thanks a lot now I´ll try to update ups firmware wish me luck.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore