Posted: 2021-06-30 04:42 AM . Last Modified: 2024-03-08 04:10 AM
We have close to 1000 UPSes with mgmt cards and it would take forever to go to each one in the GUI and uncheck the 'repeat interval' check box on every single notification. It sucks they're all checked by default. I just want 1 email notification.
I'm hoping there is a global command to uncheck all boxes and hoping knows what it is.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:43 AM . Last Modified: 2024-03-08 04:10 AM
Hi,
You can accomplish the task by editing the NMC config.ini file and then using the iniutil push the required changes to all cards.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:43 AM . Last Modified: 2024-03-08 04:10 AM
Hi,
You can accomplish the task by editing the NMC config.ini file and then using the iniutil push the required changes to all cards.
Link copied. Please paste this link to share this article on your social media post.