Need info about 'Tiers'

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Need info about 'Tiers'
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:11 AM . Last Modified: ‎2024-03-19 02:29 AM

0 Likes
5
3089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:11 AM . Last Modified: ‎2024-03-19 02:29 AM

Need info about 'Tiers'

Dear Folks,

As we know about Tiers levels of data center. But anybody has an excellent, presentation, excel sheet, or any type of info with good examples and pictures about Tiers?????

e.g. If we talk about a Tier3 data center, how 'additional or extra' UPS's or Cooling Unit we would give?

Thanks in advance.

Labels
  • Labels:
  • General Questions & Suggestions
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

0 Likes
0
3090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

the document you have is pretty good, i think the one for tier 3 is a bit off though but i could be wrong i'm not an expert.  i think you should have one ups on feed a and one on b, the description says it has redundant ups's but i do not see them in the image.  each rack should have a power feed from A and B giving the servers power redundancy.  i think that may be what that one vertical line is supposed to represent to the left of the power distribution modules but its not that clear. 

i don't believe you have redundant cooling in tier 3 but depending on the size of the room and the type of cooling units you choose you may have multiple units.  you would probably want multiple cooling units in a tier 3 set up so you could run maintenance on them without having to shut down the whole room or have it get incredibly hot.  you can sometimes compensate for one unit being down if you have other units that can step up their output.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

0 Likes
0
3089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

Dear adavid,

Yes I m totally agreed with u. The same thing I was thinking that the second power distribution module has represented as a vertical line. But yes it is not much clear. Any ways, Angela has shared with us a very good document plus I read a very good explanation for Tiers which is being shared with you.


"We now know that "Tier" ratings come in two versions: TIA-942-2 (TIA-942) and Uptime Institute Tier Standard: Topology (TS:T).

But are they really different?And if so, what are the core differences.


Well, they are different, and in some subtle but very important ways.

First, Both examine the resiliency of Power and Cooling systems.  However, TIA-942 also includes the categories of Architectural and Telecommunications. (That should be no surprise, as they are a Telecommunications Standards body).  In Truth, TS:T also includes telecommunications (cabling) to a limited degree, where multiple redundant routes are concerned (at Tier III) and routing compartmentalization (at Tier IV).  But that is the extent to which TS:T consider telecommunications.

The real core difference between the two, at the theoretical level, is what is considered the Primary source of Power to the site.  TIA-942 treats Utility Power Supply as the primary source for power.  At Tier 3 it requires N+1 Utility feed (so, a minimum of 2), and at Tier 4, 2N (Also, minimum of 2, but could require more, if 1 feed each will not suffice to provide total power to the site).  Generator power is used as a "bridge" only in the event that all Utility power is lost, with the expectation that utility power will be restored in a time shorter than there is fuel supply available to the generators.

TS:T treats on-site power generation as primary power, with utility power used as a low-cost alternative when available.  For Tier II and above, that requires redundancy in the generator set, but all are able to utilize N+1 generator set for redundancy, so long as the proper rules for down-stream power distribution are met which also provides for multiple power supply pathways under Tier III and Tier IV.  This carries some distinctions.  Under TS:T then, it is technically possible to achieve any Tier level with 0 incoming utility power feeds (So long as the site is able to provide continuous power generation, with redundancy for Tier II and above).  One key "gotcha" then when building a TS:T standard data center is to ensure that the generators are rated for either PRIME or CONTINUOUS run (as opposed to STANDBY rated).  If a PRIME generator is used, it must be de-rated by 70% of its capacity to meet the continuous run requirements (however, if agreed in writing with the manufacturer, it is possible to achieve up to 85% capacity for de-rating).  STANDBY generators are not robust enough for Tier III or Tier IV, but are suitable for Tier I and Tier II.  Generally, STANDBY generators are rated only to run 200 to 500 hours per year. (200 hours is 8 1/3 days, so by the time you reach day 9, you've hit maximum for the year.)


This distinction may seem trivial, however it is a crucial difference in the underpinning philosophy of TIA-942 compared to TS:T."


 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

0 Likes
0
3089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

Dear Folks,

As we know about Tiers levels of data center. But anybody has an excellent, presentation, excel sheet, or any type of info with good examples and pictures about Tiers?????

e.g. If we talk about a Tier3 data center, how 'additional or extra' UPS's or Cooling Unit we would give?

Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

0 Likes
0
3090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

i don't know of any pictures or presentations about data center tiers but Wikipedia has a decent table defining the differences, i don't believe i saw anything about tiers specifically in the APC white papers but they do have one on Data Center System Planning, and has a Data Center Design Planning Calculator that might give you the info you need.

it may not be exactly what you were looking for but i hope it helps some

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

0 Likes
0
3089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

Dear adavid,

I m truly appreciate your response. You have defined many things that are helpful. I just wanna share one thing..My attached file is not all an all, but clear some basic concepts.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

0 Likes
0
3091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:12 AM . Last Modified: ‎2024-03-19 02:29 AM

the document you have is pretty good, i think the one for tier 3 is a bit off though but i could be wrong i'm not an expert.  i think you should have one ups on feed a and one on b, the description says it has redundant ups's but i do not see them in the image.  each rack should have a power feed from A and B giving the servers power redundancy.  i think that may be what that one vertical line is supposed to represent to the left of the power distribution modules but its not that clear. 

i don't believe you have redundant cooling in tier 3 but depending on the size of the room and the type of cooling units you choose you may have multiple units.  you would probably want multiple cooling units in a tier 3 set up so you could run maintenance on them without having to shut down the whole room or have it get incredibly hot.  you can sometimes compensate for one unit being down if you have other units that can step up their output.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore