Need help in understanding shutdown sequence.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Need help in understanding shutdown sequence.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:25 PM . Last Modified: ‎2024-03-14 02:51 AM

0 Likes
3
2206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:25 PM . Last Modified: ‎2024-03-14 02:51 AM

Need help in understanding shutdown sequence.

Hi!

I have APC 5000XLI UPS with AP9619 NMC and some servers connected to it. There are clients (PCNS and apcupsd) installed on servers.

At now UPS configured with these defaults:

Start of Shutdown
Low Battery Duration: 2 minutes
Shutdown Delay: 20 seconds
Maximum Required Delay: 2 minutes
Basic Signaling Shutdown: Unchecked
Basic Low Battery Duration: 150 seconds
Duration of Shutdown
Sleep Time: 0.0 hours
End of Shutdown
Return Runtime Duration: 0 seconds
Return Delay: 10 seconds

I need to understand the shutdown sequence logic based on that settings:

When power fails the UPS goes on battery, when 4 (2+2) min remains it signals clients to shutdown, waits 4 min and 20 sec and turns off. Is that right?

What happens if power returns after NMC had sent shutdown signal?

Thank you in advance.

And sorry for my English.

Message was edited by: dfx

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:26 PM . Last Modified: ‎2024-03-14 02:51 AM

0 Likes
0
2207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:26 PM . Last Modified: ‎2024-03-14 02:51 AM

If you do not set up any shutdown settings on PCNS the software client will rely entirely on the low battery duration setting for deciding when to shutdown. A low battery shutdown starts when the amount of runtime remaining = the LBD setting. There is no added delays except for the shutdown delay during a low battery shutdown. This means when you have 2 minutes left of runtime, that is when the shutdown process occurs, and so you will have a total of only 2 minutes for the attached load to shut down. If your load is able to shut down within 2 minutes, then the NMC will command a UPS shutdown, the UPS will wait 20 seconds (shutdown delay), and then turn off. Once the actual shutdown command process from PCNS is issued for a shutdown, a return to power has no bearing on what happens, a shutdown is imminent.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:25 PM . Last Modified: ‎2024-03-14 02:51 AM

0 Likes
0
2207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:25 PM . Last Modified: ‎2024-03-14 02:51 AM

The NMC will send the command to all clients to shutdown at the low battery duration mark, regardless of how long the servers actually take to shutdown. With the LBD set to 2 minutes, when 2 minutes of runtime remain on the battery, the NMC will command everything to shutdown. UPS will shutdown 2:20 after that (when incorporating the shutdown delay).

If your servers take 10 minutes to shutdown, set the LBD to 11 minutes, yes.

The UPS doesn't really "wait" for any response from the server unless you have the box checked in PCNS to shutdown the UPS after that server is done shutting down. Unless that is enabled, it will turn off when the NMC tells it to, not the server.

We have a [specific version of PCNS|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SSPCNSV] that's designed for VM machines that you might be interested in taking a look at.

"So for example, if I use 11 minutes for LBD. At 11 minutes, command is sent, then based on the shutdown delay setting it would then wait for that to expire and then go offline?"
- Yes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:25 PM . Last Modified: ‎2024-03-14 02:51 AM

0 Likes
0
2207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:25 PM . Last Modified: ‎2024-03-14 02:51 AM

Hi!

I have APC 5000XLI UPS with AP9619 NMC and some servers connected to it. There are clients (PCNS and apcupsd) installed on servers.

At now UPS configured with these defaults:

Start of Shutdown
Low Battery Duration: 2 minutes
Shutdown Delay: 20 seconds
Maximum Required Delay: 2 minutes
Basic Signaling Shutdown: Unchecked
Basic Low Battery Duration: 150 seconds
Duration of Shutdown
Sleep Time: 0.0 hours
End of Shutdown
Return Runtime Duration: 0 seconds
Return Delay: 10 seconds

I need to understand the shutdown sequence logic based on that settings:

When power fails the UPS goes on battery, when 4 (2+2) min remains it signals clients to shutdown, waits 4 min and 20 sec and turns off. Is that right?

What happens if power returns after NMC had sent shutdown signal?

Thank you in advance.

And sorry for my English.

Message was edited by: dfx

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:26 PM . Last Modified: ‎2024-03-14 02:51 AM

0 Likes
0
2208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:26 PM . Last Modified: ‎2024-03-14 02:51 AM

If you do not set up any shutdown settings on PCNS the software client will rely entirely on the low battery duration setting for deciding when to shutdown. A low battery shutdown starts when the amount of runtime remaining = the LBD setting. There is no added delays except for the shutdown delay during a low battery shutdown. This means when you have 2 minutes left of runtime, that is when the shutdown process occurs, and so you will have a total of only 2 minutes for the attached load to shut down. If your load is able to shut down within 2 minutes, then the NMC will command a UPS shutdown, the UPS will wait 20 seconds (shutdown delay), and then turn off. Once the actual shutdown command process from PCNS is issued for a shutdown, a return to power has no bearing on what happens, a shutdown is imminent.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of