NMC2(AP9630) 6.2.1 to 6.4.0 Firmware Update Failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC2(AP9630) 6.2.1 to 6.4.0 Firmware Update Failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
8
7715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:47 AM

NMC2(AP9630) 6.2.1 to 6.4.0 Firmware Update Failure

The update utility was used to update 12 AP9630's from 6.2.1 to 6.4.0.  One of the cards failed the update.  The logs show the following failure info:

Transferring firmware file (2/3): OS
[11/06/16 12:35:09] 150.102.210.201: ERROR --> OS transfer failed

The card was reseated to reset it.  The web interface then would not display the homepage and referred to the logfile.  I then tried to FTP the update files starting with the bootmonitor which transferred ok.  The AOS file was then FTP'd.  The hash marks stopped after a few lines and hung never displaying a transfer complete error.  When I closed, reopened, and Telnet'd to the card again, it seems to connect but commands aren't displayed.  It will remain like this until I reseat the card again.  I tried this a couple of times.  A dir of the card shows just the old AOS 6.2.1 file but no SMUX file.  Is there a way to recover the card?

 

Thanks,

Chris

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
0
7709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

The UPS with the problem is in the same rack and another on the same subnet.  While the card was removed, I ping'd to make sure there wasn't another device using the same IP.  I may change it to another IP to see if that makes a difference since there are rare instances of devices on our network that do not respond to pings.  I'm also thinking about hard resetting it which formats the flash from what I have read.  I'll also give the console port method a shot if all else fails.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
0
7709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:47 AM

Your card seems fine so worst case you can use xmodem from the boot monitor (a bit on that in a second)

If the FTP process didn't finish, I'd worry about interference from a network middlebox or firewall. Try swapping the card into a UPS + network connection where the upgrade succeeded. Make sure to FTP in binary mode.

If that doesn't work, connect serially to the console port at 57600 baud, 8 data bits, 1 stop bit, no flow control. Keep hitting enter while reseating the card. You should get a BM> prompt. Type "xmodem" and enter, then send your file via xmodem and when it finishes type boot. Repeat for each file, aos first, then sumx.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
0
7710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

The UPS with the problem is in the same rack and another on the same subnet.  While the card was removed, I ping'd to make sure there wasn't another device using the same IP.  I may change it to another IP to see if that makes a difference since there are rare instances of devices on our network that do not respond to pings.  I'm also thinking about hard resetting it which formats the flash from what I have read.  I'll also give the console port method a shot if all else fails.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
0
7709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

Hello Chris,

In relation to what voidstar has posted, I would also recommend doing a factory reset or format on the network management card before attempting a firmware upgrade. Below is our FAQ on how to use BootMonitor to recover or upgrade an Network Management Card 2. The factory reset can be found on Steps 4 and 5.

Using Network Management Card 2 (NMC2) bootmonitor to recover/upgrade firmware

To format the network card, Press and hold the pinhole reset button down for about 20 seconds. If this is being performed correctly, you should see the status LED "pulsing" green. When the process is actually complete, the status LED will change its color and "pulse" orange. This is when it is time to let go. The NMC will continue to "pulse" orange a few times and then the status LED will go off, and the NMC will reboot.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
0
7709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

 

I tried all suggestions so far.  The bootmon transfers fine using either the upgrade utility, FTP, or XMODEM but the AOS transfer fails either way.  Here is what the system command shows.  It seems it can't save anything since even the bootmon shows Invalid Module Header! even after a successful transfer.

apc>system
E000: Success
Host Name Sync: Disabled
Name:           apc4D8832
Contact:        Unknown
Location:       Unknown
Message:
DateTime:       08/19/2009:00:01:37
User:           apc
Up Time:        0 Days 0 Hours 1 Minute
Stat:           P+ N4+ N6+ A-
Bootmon:        Invalid Module Header!
AOS:            Invalid Module Header!
App:            Invalid Module Header!

apc>

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
0
7709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

I'll give it a shot.  The same files were used for all 12 of the AP9630's that were upgraded and this one is the only one that had problems.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
0
7709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:47 AM

Just tried it again with the file you attached.  The results were the same with the Firmware Upgrade Utility.  Bootmon transferred with no problem but the OS transfer failed.  I have another board to try.  If it works, the current board will go in the scrap bin.  If not, I'll order a replacement.  This has eaten up a lot of time I don't have.  Thanks for trying.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:46 AM

0 Likes
0
7709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:46 AM

Agreed, trying the AOS again was a long shot. I've never seen the hardware fail that way but if xmodem didn't work and the file is good, I can't think of any other possibilities. Hopefully it's not a problem with the UPS itself, which you'll find out by testing the other board.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:46 AM

0 Likes
0
7709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:38 AM . Last Modified: ‎2024-03-13 12:46 AM

This has been a strange problem.  I think only recall one other similar problem in the past with a firmware upgrade.  For now, I found an old AB9617 from a Symmetra, replaced the AB9630 with it, loaded the firmware for a SmartUPS, configured it, and it is online.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore