NMC says "No UPS Found" - is this right?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC says "No UPS Found" - is this right?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
mrfixit_apc
Ensign mrfixit_apc
Ensign

Posted: ‎2021-07-01 04:52 AM . Last Modified: ‎2024-03-05 01:55 AM

0 Likes
9
9162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:52 AM . Last Modified: ‎2024-03-05 01:55 AM

NMC says "No UPS Found" - is this right?

When I log in to the http interface of the NMC (AP9630) installed in my SMT1000I it says "No UPS Found" - is this right?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

0 Likes
0
9154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

Ok, as I suspected, you're firmware is sumx v5.0.1. To work with SMT and SMX model Smart UPS, you need v5.0.3 or higher sumx.

So, we'll need to upgrade. The latest version with the blue interface is v5.1.7. Then, we have v6.0.6 on the website which offers many new features (a firewall, multi-user - simultaneous logins, advanced log export capability, SMTP enhancements, etc) and an entirely new interface.

To preview the new interface, we have a Network Management Card 2 @ testdrive.apc.com (AP9630 or AP9631 will be fine) and you can see the interface I am referring to. I only suggest to scope this out first because many people upgrade and hate it and I wouldn't want to put you through it. Once you get used to the new layout, the new features make it worth it though. Some people don't like change.

Let me know what firmware you're interested in.

SFSUMX606 is the part number on the website that you'll find for this newest firmware download. You can go to Software / Firmware, select Firmware Upgrades - UPS Network Management Cards from filter by software/firmware and then you'll find upon downloading, you should review a knowledge base first before upgrading. (Review article ID FA176047 @ FAQ).

Sorry to make this so complicated! I just want you to be well informed before upgrading and being frustrated.

Lastly, once you're ready to update, you can follow these instructions -> How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:52 AM . Last Modified: ‎2024-03-05 01:55 AM

0 Likes
0
9154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:52 AM . Last Modified: ‎2024-03-05 01:55 AM

No, its not. It is usually a firmware problem (wrong firmware installed on your management card) or a communication problem.

To start, on your AP9630, please tell me what the firmware version is. Is the interface blue? If so, tell me what you see under Administration->General->About for AOS and Application module names and versions.

If the interface is green, go under About->Network and you'll also see the same screen. I'll need the same info from it.

Let's start there. It might just be an older version that does not support SMTs and we can just simply upgrade it.

Reply

Link copied. Please paste this link to share this article on your social media post.

mrfixit_apc
Ensign mrfixit_apc
Ensign

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

0 Likes
0
9153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

Angles,

Interface is blue.

Here is the About info (I pasted it - sorry it looks a bit odd):

Hardware Factory
Model Number:AP9630
Serial Number:BA0933020973
Hardware Revision:05
Manufacture Date:08/16/2009
MAC Address:00 C0 B7 4D 96 E7
Management Uptime:0 Days 7 Hours 30 Minutes
Application Module
Name:sumx
Version:v5.0.1
Date:May 13 2009
Time:16:38:28
APC OS (AOS)
Name:aos
Version:v5.0.1
Date:Nov 25 2008
Time:12:09:34
APC Boot Monitor
Name:bootmon
Version:v1.0.0
Date:Oct 8 2008
Time:16:03:02

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

0 Likes
0
9155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

Ok, as I suspected, you're firmware is sumx v5.0.1. To work with SMT and SMX model Smart UPS, you need v5.0.3 or higher sumx.

So, we'll need to upgrade. The latest version with the blue interface is v5.1.7. Then, we have v6.0.6 on the website which offers many new features (a firewall, multi-user - simultaneous logins, advanced log export capability, SMTP enhancements, etc) and an entirely new interface.

To preview the new interface, we have a Network Management Card 2 @ testdrive.apc.com (AP9630 or AP9631 will be fine) and you can see the interface I am referring to. I only suggest to scope this out first because many people upgrade and hate it and I wouldn't want to put you through it. Once you get used to the new layout, the new features make it worth it though. Some people don't like change.

Let me know what firmware you're interested in.

SFSUMX606 is the part number on the website that you'll find for this newest firmware download. You can go to Software / Firmware, select Firmware Upgrades - UPS Network Management Cards from filter by software/firmware and then you'll find upon downloading, you should review a knowledge base first before upgrading. (Review article ID FA176047 @ FAQ).

Sorry to make this so complicated! I just want you to be well informed before upgrading and being frustrated.

Lastly, once you're ready to update, you can follow these instructions -> How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US

Reply

Link copied. Please paste this link to share this article on your social media post.

mrfixit_apc
Ensign mrfixit_apc
Ensign

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

0 Likes
0
9154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

Angela,

Many thanks for your detailed reply. I suspected that it might be a firmware issued - I will go straight to firmware v6.06 - since I am new to NMCs it's all change to me anyway!

I will post back when I get the update done to confirm success (hopefully laughing).

Reply

Link copied. Please paste this link to share this article on your social media post.

mrfixit_apc
Ensign mrfixit_apc
Ensign

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

0 Likes
0
9154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:55 AM

Angela,

The firmware upgrade went fine on the 2nd attempt. On the first attempt the last FTP login failed - I don't know why. However, I now have v6.06 firmware installed and the UPS now appears to be recognised fine. Many thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:54 AM

0 Likes
0
9154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:54 AM

Hi Angela,

I face same problem when buy new SURTD5000xli with AP9631 when try to console use web interface says "No UPS Found" 

this is copy of factory information 

Factory Information
Hardware Factory
Model Number
AP9631
Serial Number
5A1609T39601
Hardware Revision
08
Manufacture Date
03/06/2016
MAC Address
00 C0 B7 F7 67 2A
Management Uptime
0 Days 0 Hours 26 Minutes
Application Module
Name
sy
Version
v6.4.6
Date
Nov 2 2016
Time
17:25:46
APC OS (AOS)
Name
aos
Version
v6.4.6
Date
Oct 6 2016
Time
17:46:25
APC Boot Monitor
Name
bootmon
Version
v1.0.8
Date
Apr 8 2014
Time
10:59:40
need help which firmware I need to upgrade or down grade? thanks 
Anton
Indonesia
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:54 AM

0 Likes
1
9154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:53 AM . Last Modified: ‎2024-03-05 01:54 AM

Hi Anton,

You have loaded Symmetra UPS firmware onto a Smart-UPS model.

You should download part number SFSUMX646. You can go to http://www.apc.com/us/en/tools/download/ and then select Filter by Software/Firmware drop down list and choose Firmware Upgrades - UPS Network Management Card. Then look for SFSUMX646 part number on the page. Download and apply that.

Instructions for upgrading firmware are here if you need them ->http://www.apc.com/us/en/faqs/FA156047

Reply

Link copied. Please paste this link to share this article on your social media post.

NOYB-JP
NOYB-JP
Cadet

Posted: ‎2023-01-02 10:29 AM

0 Likes
0
6606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-02 10:29 AM

I'm trying to upgrade a Smart-UPS X 2000, SMX2000LV. I have updated the NMC to the following:

SUMX  v7.0.4

AOS     v7.0.4

bootmon v1.0.9

 

Based on the Firmware Revision ID number, (ID1003), I tried to update to the file SMX1003UPS_15-0.enc. The initial Current Version was ID1003UPS 07.4. The UPS portion still hasn't come back after updating the firmware via Configuration -> Firmware Updates after an hour. Any idea what I can do to get this unit operational again?

 

I have two of these identical units at the same location with dual power for all the devices.

 

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

NilsWberg
NilsWberg
Cadet

Posted: ‎2024-05-23 01:55 AM

In response to BillP
0 Likes
0
3455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-23 01:55 AM

Hi, we are facing the same problem as mentioned above, but we are pretty sure that it can not be related to the firmware. We have another ups of the same model in use and everything on these two devices is exactly same configured including the firmware.
You mentioned above, that its either an firmware or an communicaion problem and I think, we are dealing with a communication problem. You have any idea how to fix this?
Thx in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore