NMC restart loses SNMP connection

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC restart loses SNMP connection
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

0 Likes
6
1660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

NMC restart loses SNMP connection

I've got an application that monitors UPS events through the SNMP v3 agent. It works great except whenever the Network Management Card does a 'warmrestart'. When this occurs my application reports everything down, which is correct, however when the NMC has completed its startup, my application never reports everything is back online. This only occurs with the NMC warmrestart. If I reboot the UPS my application reports down and then up when the UPS is back online. After the warmrestart, the only way my application can connect to the UPS again is if I restart the application.

Is there anywhere the UPS would store information/data about the SNMP agent? I know SNMP has built in security to compare timestamps, addresses, etc...so as to verify the integrity of the requester. Perhaps after this warmrestart the SNMP agent on the UPS cannot verify the requester credentials anymore.

Any ideas would certainly help. I'm completely stumped why this is occurring. Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 10:55 PM . Last Modified: ‎2024-03-14 03:54 AM

0 Likes
0
1660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:55 PM . Last Modified: ‎2024-03-14 03:54 AM

If you continue to have this issue with the latest firmware, I suggest running Wireshark to capture the SNMPv3 traffic. If this is a timeliness issue, you should see a response that indicates "not in time window" or something like that. Or maybe the problem is something else and we can examine the traffic for other issues.

Should timeliness be the cause, I would look at the "Engine Boots" and "Engine Time" within the SNMPv3 packets. We should see the "Engine Boots" value from the network management card increase after a reboot or a warmstart.

!http://apc-forums.com/servlet/JiveServlet/download/25-3822-16534-994/timeliness.png!

Let us know how it goes.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

0 Likes
0
1660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

Hi Guy,

What model Network Management Card (NMC) are you using, what FW APP and AOS are on the card and what SNMP v3 agent are you running?

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

0 Likes
0
1660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

The NMC is a AP9617, not sure about the AOS and FW. It's never been updated since it came out of the box. Not sure how to answer the SNMP v3 question. I have SNMP v3 access turned on, on the UPS and my application is using net-snmp v3 version 5.3.1

Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

0 Likes
0
1661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

Application Module
sumx
Version: v3.5.5
Date: 05/24/2007
Time: 16:14:52



APC OS (AOS)

Name: aos
Version: v3.5.5
Date: 05/24/2007
Time: 15:44:22

Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

0 Likes
0
1661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:54 PM . Last Modified: ‎2024-03-14 03:54 AM

if you login via telnet/local serial access, the AOS and APP versions will be listed on the top right of the initial menu presented to you.

alternatively, you can locate it in the web interface under Administration->General->About. If its an older version, it will be located under Help->About System on the left hand side.

Lastly, you can also retrieve the .iso.org.dod.internet.mgmt.mib-2.system.sysDescr / .1.3.6.1.2.1.1.1 OID via SNMP for us which should give us something similar to:

APC Web/SNMP Management Card (MB:v3.9.2 PF:v3.7.0 PN:apc_hw02_aos_370.bin AF1:v3.7.0 AN1:apc_hw02_rpdu_370.bin MN:AP7941 HR:B2 SN: ZA0123456780 MD:10/07/2006)

you can remove the serial number at the end if the output if you do that method.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:55 PM . Last Modified: ‎2024-03-14 03:54 AM

0 Likes
0
1661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:55 PM . Last Modified: ‎2024-03-14 03:54 AM

ok, you are one version behind. before we guess and play around, i would try and flash the firmware to the latest which is AOS 3.6.1 and SUMX 3.5.8. it is available from http://www.apc.com/tools/download/index.cfm by choosing Firmware Upgrades - Network Management Card and choosing SFSUMX358.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 10:55 PM . Last Modified: ‎2024-03-14 03:54 AM

0 Likes
0
1661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:55 PM . Last Modified: ‎2024-03-14 03:54 AM

If you continue to have this issue with the latest firmware, I suggest running Wireshark to capture the SNMPv3 traffic. If this is a timeliness issue, you should see a response that indicates "not in time window" or something like that. Or maybe the problem is something else and we can examine the traffic for other issues.

Should timeliness be the cause, I would look at the "Engine Boots" and "Engine Time" within the SNMPv3 packets. We should see the "Engine Boots" value from the network management card increase after a reboot or a warmstart.

!http://apc-forums.com/servlet/JiveServlet/download/25-3822-16534-994/timeliness.png!

Let us know how it goes.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of