APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
I have 2 - sua2200 and 2- su1500 UPS'. They all are configured and running perfectly with NMC AP9617 cards,
One issue, my boss wants the UPS's to send "self tests" at about the same time and period every 7 days. Right now they are scattered through the week.
How do I get them to do this without doing too much invasive reprogramming?
Thanks in advance.
Brian
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
I have 2 - sua2200 and 2- su1500 UPS'. They all are configured and running perfectly with NMC AP9617 cards,
One issue, my boss wants the UPS's to send "self tests" at about the same time and period every 7 days. Right now they are scattered through the week.
How do I get them to do this without doing too much invasive reprogramming?
Thanks in advance.
Brian
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Had I known it was that easy.......
Thank you
Brian
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
I have 2 - sua2200 and 2- su1500 UPS'. They all are configured and running perfectly with NMC AP9617 cards,
One issue, my boss wants the UPS's to send "self tests" at about the same time and period every 7 days. Right now they are scattered through the week.
How do I get them to do this without doing too much invasive reprogramming?
Thanks in advance.
Brian
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.