Monitor Multiple Smart-UPS models from single server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Monitor Multiple Smart-UPS models from single server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:18 AM

0 Likes
5
2683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:18 AM

Monitor Multiple Smart-UPS models from single server

I've seen countless post regarding this but I've also seen countless answers as well.

I am looking to monitor 3 separate Smart Series UPSes fro ma single server. How would I go about doing this? Models are SC1000, SC1500, and SC450. All have serial connections. Do I need an expansion card for the server? Do I need a specific edition of PowerChute (even though it's crap)? Is there a better solution then powerchute (APCUPSD?)

Any info is welcomed.

Sorry for the same question asked previously but none of the answers are straight forward.

If I understand this correctly I should be able to use the regular PowerChute Business Edition to monitor 3 separate UPSes centrally if all are connected via Serial.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

0 Likes
0
2684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

So i was correct. The windows version of APCUPSD does not support multiple instances but it seems the Linux version does. In theory I could add two USB-SERIAL adapters into the two USB ports on the home automation controller. Install the drivers for the adapters and install APCUPSD. Then install APCUPSD windows version on the 1U Windows Server. I could then monitor all three UPSes via the 1U Windows Server. Two attached to the Linux based controller and one attached to the 1U windows Server.

That make sense?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

0 Likes
0
2683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

Hi,

If you install PowerChute Business Edition Agent on each system serially connected to the Smart-UPS you can monitor each Agent by installing the PowerChute Business Edition Server and Console on one of the system. You can then add each of the Agent to be monitored to the Server. The Console is the GUI to view the PowerChute Business Edition Server. Installation instruction are available at this link

http://www.apcmedia.com/salestools/PMAR-9BUL4B/PMAR-9BUL4B_R0_EN.zip

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

0 Likes
0
2683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

There is only one system and 3 Smart series UPSes.

Setup is as follows:

APC SMART SC 450 - Connected to Broadband Cable Modem, WLAN AP, 10 Port Switch

APC SMART SC 1000 - Connected to CCTV DVR and Cameras

APC SMART SC 1500 - Connected to Supermicro 1U Server with 3 Serial ports

I'd like to monitor the 3 UPSes on the 1U Supermicro system; How could this be accomplished?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

0 Likes
0
2683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

Hi,

You will need APCUPSD for this configuration. If you review their user's manual you will find Multiple UPS Configuration. Below is a description.

A configuration is where a single computer controls multiple UPSes. In this case, there are several instances of apcupsd on the same computer, each controlling a different UPS. One instance of apcupsd will run in standalone mode, and the other instance will normally run in network mode. This type of configuration may be appropriate for large server farms that use one dedicated machine for monitoring and diagnostics

For support woht APCUPSD you should sign up for their mail list. http://www.apcupsd.org/wordpress/email-lists/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

0 Likes
0
2683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

I did think of another option. I do have a small fan-less Linux machine in my rack too. I forgot because it's a home automation controller but it's built on a raspberry-pi and runs Debian. It does have dual USB interfaces as well. I'm thinking of possibly using a USB-Serial on that machine and the on board serial on the 1U supermicro. That would monitor the SC1000 and the SC1500. I could then just ignore the SC450 but I'll first look into APCUPSD. I sort of remember it not being able to run multiple instances on a windows server though. I guess I could have the Linux machine monitor two and have the 1U server monitor the last as an alternative.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

0 Likes
0
2685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:25 AM . Last Modified: ‎2024-03-13 04:17 AM

So i was correct. The windows version of APCUPSD does not support multiple instances but it seems the Linux version does. In theory I could add two USB-SERIAL adapters into the two USB ports on the home automation controller. Install the drivers for the adapters and install APCUPSD. Then install APCUPSD windows version on the 1U Windows Server. I could then monitor all three UPSes via the 1U Windows Server. Two attached to the Linux based controller and one attached to the 1U windows Server.

That make sense?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore