Module Breaker Open / Close Alarm

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Module Breaker Open / Close Alarm
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
sayleong_apc
Crewman sayleong_apc
Crewman

Posted: ‎2021-07-29 09:27 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
7
4331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:27 PM . Last Modified: ‎2024-02-14 02:33 AM

Module Breaker Open / Close Alarm

We deployed APC Symmeta 48K with 3 units of PDM (model PDM2332IEC-3P30R-1). Each PDM has three miniature circuit breaker with load of 32A each.

1. In Nov 2014, we have the critical error message - "module breaker - open alarm Mod[3].L2" - pls see attachment. But there is no tripped and all power to rack PDU are ok. None of the servers are down. Strange.

Within minutes, we noticed the error message cleared when breaker is "CLOSED". There is red blinking LED at the PDM and then moment later, it turns green. This sequence is repeated continuously until TODAY and still happening.

2. Last month, we have the same critical error message  "module breaker - open alarm Mod[5].L3" - pls see attachment. So, this time, it on another PDM and another circuit breaker within that PDM. Again, I can see there is blinking RED LED at the PDM and then moment later, it turns green. This sequence is repeated continuously until TODAY and still happening. But, we do not experience power tripped and none of our servers are down.

Strange? Can someone please enlighten?  

Attachments
Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi again,

I suggest that you contact your local escalation for further detail. We just don't have the expertise on the forum with these products specifically to be able to support your question to the level of detail that I think you need and should be able to get. I am under the assumption that there may be an issue your local support is aware of and could go into further detail about specific to your installation.

Because of my lack of expertise with this type of product, I don't quite know how to answer your second question either. I am not sure at what level components are replaced either.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:27 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:27 PM . Last Modified: ‎2024-01-31 02:55 AM

Hello,

I asked our EMEA tech support regarding this as they deal with those types of PDMs. They advised to contact your local support as this may indicate the particular PDM or some component may require replacement if it is showing this type of symptom.

Reply

Link copied. Please paste this link to share this article on your social media post.

sayleong_apc
Crewman sayleong_apc
Crewman

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
0
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

Thank you for your prompt reply, Angela.

Well, indeed it may be that particular PDM unit or one of miniature circuit breakers within that particular PDM unit is "faulty" and require replacement. Hence, the critical error message shown up.

However, I hope you can of assistance --- so, if these kind of error message shown up and yet, "it seems like nothing happening to the power line, or rack PDU or my servers", how can I convince my management that PDM LED light is blinking red and suddenly turns green again and turns red again while there is no power trip ---- still we NEED to shutdown affected rack PDU / server in order to investigate it is really PDM issue or one of miniature circuit breaker issue and therefore require replacement? 

Another matter. perhaps you can share --- what kind of test or tools they used is carried out by qualified Schneider engineer to track and investigate PDM issue / miniature circuit breaker issue? --- it is for my learning knowledge. Appreciate your time and effort.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
4326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

Hi again,

I suggest that you contact your local escalation for further detail. We just don't have the expertise on the forum with these products specifically to be able to support your question to the level of detail that I think you need and should be able to get. I am under the assumption that there may be an issue your local support is aware of and could go into further detail about specific to your installation.

Because of my lack of expertise with this type of product, I don't quite know how to answer your second question either. I am not sure at what level components are replaced either.

Reply

Link copied. Please paste this link to share this article on your social media post.

sayleong_apc
Crewman sayleong_apc
Crewman

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
0
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

Hi Angela,

Thanks for your reply. Noted. Sure, we will engage Malaysia Schneider engineer on this matter.  

Reply

Link copied. Please paste this link to share this article on your social media post.

AndreD_apc
AndreD_apc
Cadet

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
0
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:33 AM

Hello Say Leong , You have solved your problem with the error "module breaker - open alarm Mod[3].L2"? I had the same problem. I can't find a solution.Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

sayleong_apc
Crewman sayleong_apc
Crewman

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-02-14 02:22 AM

Well, unfortunately not. So, till today, the issue remains. 

I am guessing my PDM or miniature breaker is something wrong yet not to the extend that is impacting my PDU or power line. So, I will leave it as it is. 

It is really hard to schedule downtime for my data center and from time to time we have re-org. So, it's kind of messy. Maybe, out of 3 PDM I have,  I can try to identify which affected servers for PDM

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

0 Likes
0
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 09:28 PM . Last Modified: ‎2024-01-31 02:55 AM

For you info, i experience the same on a symetra PX160. I will follow you, i don't touch as it doesn't affect the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of