Hello,
I have installed a network management card in my APC3000RM
I was able to browse to the card and configure settings, but was having problems setting up the PCNS.
So.... I upgraded the firmware on the NMC to version 5.11.
Now when I login it tells me the UPS is online on the Home tab, but i am now missing the entire UPS tab.
The UPS tab was there before the upgrade..... ๐
I have not yet rebooted the whole UPS just the management card.
Details from General/About below -
Hardware Factory
Model Number: AP9630
Serial Number: BA0930018235
Hardware Revision: 05
Manufacture Date: 07/24/2009
MAC Address: 00 C0 B7 4D 09 94
Management Uptime: 0 Days 0 Hours 6 Minutes
Application Module
Name: sy
Version: v5.1.1
Date: Jan 22 2010
Time: 12:24:34
APC OS (AOS)
Name: aos
Version: v5.1.1
Date: Dec 10 2009
Time: 10:12:00
APC Boot Monitor
Name: bootmon
Version: v1.0.1
Date: Aug 3 2009
Time: 16:30:40
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-28 11:55 PM . Last Modified: โ2024-03-14 01:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-28 11:55 PM . Last Modified: โ2024-03-14 01:11 AM
Yes, the latest Firmware Version is 5.1.1 only but the part number to download is SFSUMX511 "Network Management Card v5.1.1 Firmware for Smart-UPS with AP9630/3". Please reflash the new firmware on it and check.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-28 11:55 PM . Last Modified: โ2024-03-14 01:12 AM
I'd try reflashing the firmware first. It could've been a bad flash or something... If that doesn't fix it, then we might have to try reseating the card or messing with the UPS, which would require you to turn off your equipment. Get the less intrusive troubleshooting out of the way first though!
As a side note, the firmware on the card shouldn't affect your success (or lack thereof) with PCNS. What was the issue there?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-28 11:55 PM . Last Modified: โ2024-03-14 01:11 AM
buzz,
Is the APC3000RM a SmartUPS?
If so, then it sounds like Jim flashed the Symmetra app onto his NMC card. He would be better served upgrading to the [latest SmartUPS NMC app shown here|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=suA3000RMI2U&tab=Software].
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-28 11:55 PM . Last Modified: โ2024-03-14 01:11 AM
Oops you're right - sorry, I didn't even notice. That'll teach me to multitask...
Yes, jim flashed the wrong firmware to the card - you have a Smart-UPS but put Symmetra firmware on the card, which is why it doesn't recognize the UPS. You want the SFSUMX511 download listed in the link void provided.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-28 11:55 PM . Last Modified: โ2024-03-14 01:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-28 11:55 PM . Last Modified: โ2024-03-14 01:11 AM
Yes, the latest Firmware Version is 5.1.1 only but the part number to download is SFSUMX511 "Network Management Card v5.1.1 Firmware for Smart-UPS with AP9630/3". Please reflash the new firmware on it and check.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.