Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Meaning of "Load Current"
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:29 PM. Last Modified: 2024-03-1404:27 AM
Meaning of "Load Current"
Hi,
we are running several "IBM UPS 3000XHV" with an APC-Management interface.
In the interface the UPS shows a number named "Load Current", which should show the Ampere the UPS currently uses.
This number seems to be nearly statical on all USVs and is constant for some days on 3 of 5 systems.
Does this number reliable show the current load?
Can I calculate Watt by multiplying Voltage with Ampere?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:29 PM. Last Modified: 2024-03-1404:27 AM
Stephan,
The Output Current shows the current in amperes drawn by the load of the UPS. If the load connected to the UPS is less than one ampere, this value shows 0 A. This is due to the UPS units ability to measure small loads accurately. With small loads, the rate of accuracy is low. With a larger load, the UPS will provide a more accurate load rating.
I recommend you to upgrade the Network Management Interface firmware if it has got an older firmware version. This is a normal practice if you feel that the card shows erroneous report.
As far as I know, we can only calculate the VA(Volt-Amps) by multiplying Voltage with Ampere.
VA=Voltage(V) X Amps(I)
Watts=VA X Power Factor (P.F)
You can see the percentage of the output Watt(%Wout ) value through the Network Management web interface.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:29 PM. Last Modified: 2024-03-1404:27 AM
Stephan,
The Output Current shows the current in amperes drawn by the load of the UPS. If the load connected to the UPS is less than one ampere, this value shows 0 A. This is due to the UPS units ability to measure small loads accurately. With small loads, the rate of accuracy is low. With a larger load, the UPS will provide a more accurate load rating.
I recommend you to upgrade the Network Management Interface firmware if it has got an older firmware version. This is a normal practice if you feel that the card shows erroneous report.
As far as I know, we can only calculate the VA(Volt-Amps) by multiplying Voltage with Ampere.
VA=Voltage(V) X Amps(I)
Watts=VA X Power Factor (P.F)
You can see the percentage of the output Watt(%Wout ) value through the Network Management web interface.