Matrix Smartcell Battery Replacement Reset Help...

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix Smartcell Battery Replacement Reset Help...
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:25 PM . Last Modified: β€Ž2024-03-15 02:45 AM

0 Likes
9
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:25 PM . Last Modified: β€Ž2024-03-15 02:45 AM

Matrix Smartcell Battery Replacement Reset Help...

Hi, I have a Matrix 5000 208V with 2 Smartcell battery packs. Over the past month both replacement lights have come on and the Matrix is displaying 2 bad battery packs. I went out and purchased replacement 18Ah batteries, and I have replaced them to the original config. My Matrix is working fine now, but it is still indicating the 2 bad packs, and the lights on the smartcells are still lit.

How can I reset the Smartcells? I dont care to change the date (although that would be helpful too), I just want to get rid of the warnings and warning lights (w/o clipping the wires πŸ™‚ )

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

"Thanks for the help, that seems complicated enough to work. I will let you know how it goes.

Thanks!"

Lol, ok that was pretty funny, I'm going to have to use that!

Stew

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:25 PM . Last Modified: β€Ž2024-03-15 02:45 AM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:25 PM . Last Modified: β€Ž2024-03-15 02:45 AM

Thanks for the help, that seems complicated enough to work. I will let you know how it goes.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:25 PM . Last Modified: β€Ž2024-03-15 02:45 AM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:25 PM . Last Modified: β€Ž2024-03-15 02:45 AM

I have some frustrating news for those that soldered to the chip or shorted it directly.

There is a place ON the board to short that is designed for this procedure.

In the picture posted earlier it is also present there as well, only it's unfortunately hidden under his serial number label.

look closely and at the top center of the board, you will see a place to solder in a push button switch.

It's labelled "SW 1", and its between the data ports.

Short the two smaller solder pads and that's better and safer than shorting in any other location.smile

No other components are required, just a switch and some solder.

I recommend a right angle PCB switch like this one...

http://www.rapidonline.com/catalogueimages/module/M077306P01WL.jpg

Then, follow the most revised directions above in this thread.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:25 PM . Last Modified: β€Ž2024-03-15 02:45 AM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:25 PM . Last Modified: β€Ž2024-03-15 02:45 AM

the part number "SMARTCELL" technically does not have user replaceable batteries. there isnt really a reset procedure because you are supposed to replace the entire casing. the only thing you could try is maybe a UPS self test which maybe you have already done that.

the part number "SMARTCELL-XR" (extended run battery pack) does have user replaceable batteries. each XR takes a quantity 1 of RBC14 (which is 4 battery cells). this SMARTCELL-XR does have a reset procedure for the replace battery LED and also a removable/replaceable communication unlike the standard SMARTCELL batteries.

so essentially, since you have a regular SMARTCELL, there is no reset procedure and the entire case would need to be replaced (since there are no user replaceable parts) - thus you'd have to buy a new SMARTCELL which includes batteries. you cannot buy the case separate from the batteries.

sorry, i'm sure thats not what you want to hear 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:45 AM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:45 AM

[Here is solution|http://apc-fix.com/page.php?id=98] ( Translation from Russian required )

If that did not help,

Try:

1) Matrix turned ON, SmartCell connected to UPS all connectors ( power & data cables )
2) unplug data cable from SmartCell
3) Wait until led on SmartCell stop shining
4) Short EEPROM IC3 pin8 - 5V to IC2 CPU pin 17 ( it's like you press reset button on SmartCell XR )
5) plug in SmartCell data cable to Matrix main unit
6) led on SmartCell start flashing
7) wait 5 sec.
8) Turn Matrix OFF
9) Remove junction EEPROM IC3 pin8 - 5V to IC2 CPU pin 17
10) Done

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:45 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:45 AM

This is a pretty ingenious solution, but please keep in mind that if you decide to follow this solution, APC will not support any damage caused in the process nor be liable for any incident or injury that occurs. In any case, that's good input!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

I just wanted to add that the instructions worked for me but they were not exactly correct. Maybe I have a newer or older Matrix.
Anyway I wanted to post up exactly what worked for me in case any one comes across this later.

First of all, There was no easy way to get access to the Chip. There was no cover over the chip. I had to take the entire rear section out to get access. While I had it out, I went ahead and soldered wire to each pin of the chip as mentioned above. 17 and 28. I then installed a small panel mount momentary switch in the front of the casing up near the LED up front.
I did this so that I could more easily reset the circuit the next time I replaced the batteries.

As I said, the instructions didn't quite work the same way as detailed in the post above.
Here is what DID work for me for me though.
1) Start with nothing plugged into the Matrix UPS from the battery pack, no Power or Data cables. the Matrix UPS should be up and running as normal.
2) Short circuit pins 17 and 28. I do this with my push button switch I installed.
3) Plug in battery pack Power cable to the Matrix.
4) Plug in the battery pack data cable to the Matrix.
5) The LED will begin to flash.
6) Remove the Jumper between pins 17 and 28 ( or release the button in my case)
7) Unplug Data cable from Matrix
8) Unplug battery pack power cable from matrix.
9) Wait for LED to stop flashing.
10) Plug in the power and data cables from battery pack to the Matrix.

Reply

Link copied. Please paste this link to share this article on your social media post.

nexxt_apc
Crewman nexxt_apc
Crewman

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

Thanks a lot, Kabak! Your solution works!

We have made some R&D and found that this can be made easier, here it is:

0) unscrew the small metal plate below Data Connectors. You'll get access to the CPU chip
1) Matrix turned ON, SmartCell connected to UPS all connectors ( power & data cables )
2) unplug data cable from SmartCell
3) Wait until led on SmartCell stop shining
4) Short CPU pins 17 and 28
5) plug in SmartCell data cable to Matrix main unit
6) led on SmartCell start flashing
7) Remove junction CPU pin 17-28
8) unplug data cable from SmartCell
9) Unplug the SmartCell's POWER cable
10) Done

Message was edited by: nexxt

better picture

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

nexxt_apc
Crewman nexxt_apc
Crewman

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

please keep in mind that if you decide to follow this solution, APC will not support any damage caused in the process nor be liable for any incident or injury that occurs
ABSOLUTELY!
Smartcell is a NON-SERVICABLE battery and anything you do about it is an EXPERIMENT!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

0 Likes
0
2012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:26 PM . Last Modified: β€Ž2024-03-15 02:44 AM

"Thanks for the help, that seems complicated enough to work. I will let you know how it goes.

Thanks!"

Lol, ok that was pretty funny, I'm going to have to use that!

Stew

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of