Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
I have just installed two new Smartcells my MATRIX 5000 UPS.
Everything was fine until i ran a runtime calibration.
Now i constantly have the alert (red "X") saying:
Discharged Battery
The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
I cant make this go away.
The batteries are charging fine from the runtime calibration test, nothing seems wrong.
What did I do?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
It turns out that after a night of charging, and with production load applied at 46%, I ran a calibration and the discharged battery alert is now gone!
However, 12 hours later I now get...
06/01/2013 11:46:52 UPS: A faulty battery no longer exists.
06/01/2013 11:46:37 UPS: At least one faulty battery exists.
06/01/2013 11:23:41 UPS: A faulty battery no longer exists.
06/01/2013 11:23:25 UPS: At least one faulty battery exists.
06/01/2013 11:20:52 UPS: A faulty battery no longer exists.
06/01/2013 11:20:36 UPS: At least one faulty battery exists.
06/01/2013 11:17:31 UPS: A faulty battery no longer exists.
06/01/2013 11:17:16 UPS: At least one faulty battery exists.
06/01/2013 11:12:09 UPS: A faulty battery no longer exists.
06/01/2013 11:11:53 UPS: At least one faulty battery exists.
06/01/2013 11:07:45 UPS: A faulty battery no longer exists.
06/01/2013 11:07:29 UPS: At least one faulty battery exists.
Argh!!!!!!!
I will mark this answered and post this new error as another question (link below)....
Matrix 5000 faulty battery alert comes and goes constantly in new smartcell.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
I'll reply based on the conditions at the time I posted the question...
How long ago did the calibration end?
2 hours
What is the current battery capacity?
77%
What is the current battery voltage?
55 volts
What is the current estimated runtime?
ZERO
What is the load % displayed on the UPS?
43%
What is the low battery warning set to?
There is no setting for this that I can see, however this ups is configured exactly the same as the other Matrix next to it that doesn't have new batteries or this problem.
As of this morning, with 9% load, ( I removed the production equipment from it last night) it sits with no error at 100% and an 18 minute run-time.
However 18 minutes has got to be wrong and to me still indicates a problem.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
Is the Matrix correctly reporting Number of Smartcells ? Otherwise, you could try a manual calibration of the UPS. Manual cal is done by putting a 25 % load on it, pull the plug and let it run til battery exhaustion/shutdown, and then let it recharge completely.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
Yes, it knows there are 2 smartcells. So no error there.
If it persists, I will do the manual calibration for sure. thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
It turns out that after a night of charging, and with production load applied at 46%, I ran a calibration and the discharged battery alert is now gone!
However, 12 hours later I now get...
06/01/2013 11:46:52 UPS: A faulty battery no longer exists.
06/01/2013 11:46:37 UPS: At least one faulty battery exists.
06/01/2013 11:23:41 UPS: A faulty battery no longer exists.
06/01/2013 11:23:25 UPS: At least one faulty battery exists.
06/01/2013 11:20:52 UPS: A faulty battery no longer exists.
06/01/2013 11:20:36 UPS: At least one faulty battery exists.
06/01/2013 11:17:31 UPS: A faulty battery no longer exists.
06/01/2013 11:17:16 UPS: At least one faulty battery exists.
06/01/2013 11:12:09 UPS: A faulty battery no longer exists.
06/01/2013 11:11:53 UPS: At least one faulty battery exists.
06/01/2013 11:07:45 UPS: A faulty battery no longer exists.
06/01/2013 11:07:29 UPS: At least one faulty battery exists.
Argh!!!!!!!
I will mark this answered and post this new error as another question (link below)....
Matrix 5000 faulty battery alert comes and goes constantly in new smartcell.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
Do either of the two smart cells have their red fault LED turned on ?
what management card are u using and what firmware rev is it at ? I am wondering if the management card is
is giving false alerts ....
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
No red lights - i would have re-run the reset procedure if I saw that.
Here is the other data...
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
No problem with the web card firmware at least; that's the latest and greatest rev. You could try disconnecting one of the smartcell batteries at a time and see if the problem goes away ...or maybe you already tried that ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
I am out of town for a week, and i silenced the email alerts for the time being, since i know it's actually not broken.
I will try this ASAP upon my return next week.
More to come...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:55 AM . Last Modified: 2024-03-13 12:18 AM
When i promised "More to come..." apparently I dropped the ball there.
I hate unfinished threads, so here is the conclusion (years later)
The Smartcell communication cables (the "phone handset" sized ones) has at least one that was bad.
I have since rebuilt these units AGAIN and all is good.
Don't underestimate that those comm cables can go bad!!! (What a headache)