Matrix 5000 w/2 new smartcells, always says "Discharged Battery: The battery power is too low to support the load"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix 5000 w/2 new smartcells, always says "Discharged Battery: The battery power is too low to support the load"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
9
1925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

Matrix 5000 w/2 new smartcells, always says "Discharged Battery: The battery power is too low to support the load"

I have just installed two new Smartcells my MATRIX 5000 UPS.

Everything was fine until i ran a runtime calibration.

Now i constantly have the alert (red "X") saying:

Discharged Battery

The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.


I cant make this go away.

The batteries are charging fine from the runtime calibration test, nothing seems wrong.


What did I do?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

It turns out that after a night of charging, and with production load applied at 46%, I ran a calibration and the discharged battery alert is now gone!

However, 12 hours later I now get...

06/01/2013     11:46:52     UPS: A faulty battery no longer exists.

06/01/2013     11:46:37     UPS: At least one faulty battery exists.

06/01/2013     11:23:41     UPS: A faulty battery no longer exists.

06/01/2013     11:23:25     UPS: At least one faulty battery exists.

06/01/2013     11:20:52     UPS: A faulty battery no longer exists.

06/01/2013     11:20:36     UPS: At least one faulty battery exists.

06/01/2013     11:17:31     UPS: A faulty battery no longer exists.

06/01/2013     11:17:16     UPS: At least one faulty battery exists.

06/01/2013     11:12:09     UPS: A faulty battery no longer exists.

06/01/2013     11:11:53     UPS: At least one faulty battery exists.

06/01/2013     11:07:45     UPS: A faulty battery no longer exists.

06/01/2013     11:07:29     UPS: At least one faulty battery exists.



Argh!!!!!!!


I will mark this answered and post this new error as another question (link below)....


Matrix 5000 faulty battery alert comes and goes constantly in new smartcell.


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

I'll reply based on the conditions at the time I posted the question...

How long ago did the calibration end?

2 hours

What is the current battery capacity?

77%

What is the current battery voltage?

55 volts

What is the current estimated runtime?

ZERO

What is the load % displayed on the UPS?

43%

What is the low battery warning set to?

There is no setting for this that I can see, however this ups is configured exactly the same as the other Matrix next to it that doesn't have new batteries or this problem.

As of this morning, with 9% load, ( I removed the production equipment from it last night) it sits with no error at 100% and an 18 minute run-time.

However 18 minutes has got to be wrong and to me still indicates a problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

Is the Matrix correctly reporting Number of Smartcells ?  Otherwise, you could try a manual calibration of the UPS. Manual cal is done by putting a 25 % load on it, pull the plug and let it run til battery exhaustion/shutdown, and then let it recharge completely.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

Yes, it knows there are 2 smartcells.  So no error there.

If it persists, I will do the manual calibration for sure.  thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

It turns out that after a night of charging, and with production load applied at 46%, I ran a calibration and the discharged battery alert is now gone!

However, 12 hours later I now get...

06/01/2013     11:46:52     UPS: A faulty battery no longer exists.

06/01/2013     11:46:37     UPS: At least one faulty battery exists.

06/01/2013     11:23:41     UPS: A faulty battery no longer exists.

06/01/2013     11:23:25     UPS: At least one faulty battery exists.

06/01/2013     11:20:52     UPS: A faulty battery no longer exists.

06/01/2013     11:20:36     UPS: At least one faulty battery exists.

06/01/2013     11:17:31     UPS: A faulty battery no longer exists.

06/01/2013     11:17:16     UPS: At least one faulty battery exists.

06/01/2013     11:12:09     UPS: A faulty battery no longer exists.

06/01/2013     11:11:53     UPS: At least one faulty battery exists.

06/01/2013     11:07:45     UPS: A faulty battery no longer exists.

06/01/2013     11:07:29     UPS: At least one faulty battery exists.



Argh!!!!!!!


I will mark this answered and post this new error as another question (link below)....


Matrix 5000 faulty battery alert comes and goes constantly in new smartcell.


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

Do either of the two smart cells have their red fault LED  turned on ?

what management card are u using and what firmware rev is it at ? I am wondering if the management card is

is giving false alerts ....

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

No red lights - i would have re-run the reset procedure if I saw that.

Here is the other data...

1212_pastedImage_16.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

No problem with the web card firmware at least; that's the latest and greatest rev.smile    You could try disconnecting one of the smartcell batteries at a time and see if the problem goes away ...or maybe you already tried that ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

I am out of town for a week, and i silenced the email alerts for the time being, since i know it's actually not broken.

I will try this ASAP upon my return next week.

More to come...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

When i promised "More to come..." apparently I dropped the ball there.

I hate unfinished threads, so here is the conclusion (years later)

The Smartcell communication cables (the "phone handset" sized ones) has at least one that was bad.

I have since rebuilt these units AGAIN and all is good.

Don't underestimate that those comm cables can go bad!!! (What a headache)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore