Matrix 5000 faulty battery alert comes and goes constantly in new smartcell.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix 5000 faulty battery alert comes and goes constantly in new smartcell.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
5
776
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

Matrix 5000 faulty battery alert comes and goes constantly in new smartcell.

It turns out that after a night of charging, a new set of smartcells, I ran a calibration with 46% (normal) and the UPS operates like new!

However, 12 hours later I now get...

06/01/2013     11:46:52     UPS: A faulty battery no longer exists.

06/01/2013     11:46:37     UPS: At least one faulty battery exists.

06/01/2013     11:23:41     UPS: A faulty battery no longer exists.

06/01/2013     11:23:25     UPS: At least one faulty battery exists.

06/01/2013     11:20:52     UPS: A faulty battery no longer exists.

06/01/2013     11:20:36     UPS: At least one faulty battery exists.

06/01/2013     11:17:31     UPS: A faulty battery no longer exists.

06/01/2013     11:17:16     UPS: At least one faulty battery exists.

06/01/2013     11:12:09     UPS: A faulty battery no longer exists.

06/01/2013     11:11:53     UPS: At least one faulty battery exists.

06/01/2013     11:07:45     UPS: A faulty battery no longer exists.

06/01/2013     11:07:29     UPS: At least one faulty battery exists.

ARGH!!!!

Below is the status and firmware information....

Status

Last Battery Transfer:         Due to software command or UPS's test control

Internal Temperature:          72.5°F

Runtime Remaining:          1 hour 43 minutes

Power

Input Voltage:               241.2 VAC

Output Voltage             235.6 VAC

Frequency:                    60.00 Hz

Load

Load Power:                    15.0 %Watts

Apparent Load Power:       11.6 %VA

Load Current:                    3.49 Amps

Battery

Capacity:              100.0 %

Battery Voltage:     55.90 VDC

Batteries:               2

Bad Batteries:        0



1213_pastedImage_0.png

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:56 AM . Last Modified: ‎2024-03-13 12:17 AM

0 Likes
0
776
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:56 AM . Last Modified: ‎2024-03-13 12:17 AM

SOLUTION FOUND!!!!!!!!!!!!!!!!
WHY OH WHY didn't I CHECK THE BATTERY COMMUNICATION CABLES?!?!?!?!?!

That was the situation.

I opened a new bag of them and replaced them - the problem vanished.

I suspect this is what cause a thermal runaway condition that melted the batteries before somehow too.

SO PLEASE REPLACE THOSE OLD COMM CABLES IF YOU GET THIS!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

0 Likes
0
776
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:18 AM

Hi, when you acquired these smartcells as "rebuilt", did the seller mention whether he/she had cleared the flash memory (reset) the smartcell's built in intelligence/communications card ? If they didn't do that, you will never get a healthy cell indication from the matrix for that module.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:17 AM

0 Likes
0
776
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:17 AM

It turns out that after a night of charging, a new set of smartcells, I ran a calibration with 46% (normal) and the UPS operates like new!

However, 12 hours later I now get...

06/01/2013     11:46:52     UPS: A faulty battery no longer exists.

06/01/2013     11:46:37     UPS: At least one faulty battery exists.

06/01/2013     11:23:41     UPS: A faulty battery no longer exists.

06/01/2013     11:23:25     UPS: At least one faulty battery exists.

06/01/2013     11:20:52     UPS: A faulty battery no longer exists.

06/01/2013     11:20:36     UPS: At least one faulty battery exists.

06/01/2013     11:17:31     UPS: A faulty battery no longer exists.

06/01/2013     11:17:16     UPS: At least one faulty battery exists.

06/01/2013     11:12:09     UPS: A faulty battery no longer exists.

06/01/2013     11:11:53     UPS: At least one faulty battery exists.

06/01/2013     11:07:45     UPS: A faulty battery no longer exists.

06/01/2013     11:07:29     UPS: At least one faulty battery exists.

ARGH!!!!

Below is the status and firmware information....

Status

Last Battery Transfer:         Due to software command or UPS's test control

Internal Temperature:          72.5°F

Runtime Remaining:          1 hour 43 minutes

Power

Input Voltage:               241.2 VAC

Output Voltage             235.6 VAC

Frequency:                    60.00 Hz

Load

Load Power:                    15.0 %Watts

Apparent Load Power:       11.6 %VA

Load Current:                    3.49 Amps

Battery

Capacity:              100.0 %

Battery Voltage:     55.90 VDC

Batteries:               2

Bad Batteries:        0



1213_pastedImage_0.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:17 AM

0 Likes
0
776
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:17 AM

Thanks, I'll do this!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:17 AM

0 Likes
0
776
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:55 AM . Last Modified: ‎2024-03-13 12:17 AM

It is now 2016...

I know that this is a few years later, but these APC Matrix units are still doing well at client sites.
So IK wanted to close the door on this issue and now am trying to diagnose what actually happened here.

Is there a set of tests I can run to validate that the Matrix 5000 unit in this thread is not going to kill another set of cells?

Some voltage / charger / inverter tests i can perform?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:56 AM . Last Modified: ‎2024-03-13 12:17 AM

0 Likes
0
777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:56 AM . Last Modified: ‎2024-03-13 12:17 AM

SOLUTION FOUND!!!!!!!!!!!!!!!!
WHY OH WHY didn't I CHECK THE BATTERY COMMUNICATION CABLES?!?!?!?!?!

That was the situation.

I opened a new bag of them and replaced them - the problem vanished.

I suspect this is what cause a thermal runaway condition that melted the batteries before somehow too.

SO PLEASE REPLACE THOSE OLD COMM CABLES IF YOU GET THIS!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of