Matrix 5000 battery constant reset

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix 5000 battery constant reset
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

0 Likes
2
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

Matrix 5000 battery constant reset

I have a matrix 5000 at home... protecting core lighting and fridge/freezers and various computer equipment.  It has had several configurations (including my own string of batteries at one point).  The last configuration was one extended smartcell that was getting pretty sad.

Recently, I got paid, so I bought a new empty smartcell (total of 2) and refilled the first smartcell with new CSB's.  Both smartcells are connected and known to the UPS to be good.  The system has about a 25% load on it most of the time and is only calculating a 30 minute runtime (should be several hours).  Every time the UPS cuts in to change voltage, the time estimate goes below 5 minutes and warnings abound.  Note that the batteries are good and it can run at 20-ish percent load for several hours (has done in recent memory).

Thus I would like to reset the "battery constant".  The instructions say to connect a serial cable (done) and to use apctest.  They say the sequence is roughly given at the bottom of this post.  In my attempts (keep in mind there is a 4-5 second pause after the first '1'), this is how it goes:

Select function number: 6

Enter an ESC character (or ctl-[) to exit.

YSM
1NA
1NA
021
+NA
+NA
^[

Note that the second '1' doesn't say "PROG".  The '0' does say '21' ... which might be the current constant (the doc says it should be 'B0'... and '+' just gets me 'NA' ...

Proceedure.

1.Shutdown the apcupsd daemon;2.Run apctest;3.Choose option 6 to enter terminal mode;4.Enter Y (UPS should respond SM);5.Enter 1 (one, not el; wait 4 seconds);6.Enter 1 (one, not el; UPS should respond PROG);7.Enter 0 (zero, not oh; UPS should respond with current constant);8.Write down the existing value so that if something goes wrong, you can at least put it back to thatvalue;9.Enter + (plus) or - (minus) to increment/decrement the value;10.Enter R to reprogram constant value (UPS should respond Bye);11.Enter Y (UPS should respond SM);12.Enter 0 (zero, not oh; UPS should respond with the new constant);13.Enter Esc to exit terminal mode;14.Choose option 7 to exit apctest.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

0 Likes
0
958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

Thanks for the reply.  Oi.  Then begs the question: do I really want to do that.  It seems like the runtime estimate has slowly crawled back to regular territory.  The only worry I have is that the short interruptions it makes to adjust the voltage don't really have a positive effect on this parameter.

I do sorta need to replace the transformer fan --- but I say sorta because the "temp" of the UPS is a healthy 18C ... and it seems to stay under 20C even when supplying load.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

0 Likes
0
958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

Hello, 

The constant reset procedure you posted works only for third generation smart ups units (eg. SU700/1000/1400/2200 etc...). Matrix units are second generation, thus requiring different procedure to reset the constants. I sadly do not own a working matrix myself, but *I suspect it might* require a jumper wire similar to the second gen. Smart ups units described here:

https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/bd-p/datacenter-forum

Remember to experiment with this carefully and only at your own risk. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

0 Likes
0
959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

Thanks for the reply.  Oi.  Then begs the question: do I really want to do that.  It seems like the runtime estimate has slowly crawled back to regular territory.  The only worry I have is that the short interruptions it makes to adjust the voltage don't really have a positive effect on this parameter.

I do sorta need to replace the transformer fan --- but I say sorta because the "temp" of the UPS is a healthy 18C ... and it seems to stay under 20C even when supplying load.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of