Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-17 02:41 AM
Hi All,
I have an MGE Galaxy 3500 20kVA UPS that has an AP9631 NMC which I presume is now faulty because the NMC keeps reporting that the UPS is on battery when its actually not on battery.
We cannot Log onto the NMC as it says Invalid Username or password however the credentials are correct because we used the very same credentials when we upgraded the Firmware to v7.12 when this problem of incorrect alerts started.
The client has a spare AP9631 NMC I want to use to replace the embedded NMC as they are not prepared to buy another NMC at the moment. I am avoiding Hard Resetting the Network Card at this point incase I wont be able to reconfigure the Card as monitoring this UPS is crucial.
Please advise which Firmware needs to be loaded on the AP9631 NMC so that we can use it on this UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-17 07:22 AM
Based on your statement above are you sure you installed the correct NMC firmware for the UPS hardware?!?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-20 03:45 AM
Hi @Teken ,
Yes, I am sure I installed the correct firmware. The Firmware was pushed through to the NMC via DCE.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.