Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Lost Communication With UPS
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2811:18 AM. Last Modified: 2024-03-1505:42 AM
Lost Communication With UPS
Good afternoon! Often there are problems in the APC program PowerShute loses contact with the UPS. In the device manager, the UPS is visible installed. The cables were replaced. The problem is fixed for a while and then reappears. How can I solve the problem? Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2811:18 AM. Last Modified: 2024-03-1505:42 AM
Hi,
What is recorded in the event log? Is PowerChute recording enabling Green Mode and then comm is lost? If so, disable Green Mode, restart the PowerChute service and that should resolve the issue.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2811:18 AM. Last Modified: 2024-03-1505:42 AM
Hi,
What is recorded in the event log? Is PowerChute recording enabling Green Mode and then comm is lost? If so, disable Green Mode, restart the PowerChute service and that should resolve the issue.