Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

ATS /UPS Combination

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ATS /UPS Combination
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
5
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

ATS /UPS Combination

I would like to know thoughts on an ATS / UPS combination that i think will solve a problem we have in smaller cabinet installations at one of our sites, let me explain...

So I have a site that has around 40 UPS's on-site.  We have had a times where a UPS has failed (SMX1500RMI2UNC) and stopped outputting power.  Unfortunately this is on a production line which we cannot afford to be down.  At the moment we have a SBP1500RMI installed but when we call site facilities and ask them to move the bypass over, they don't like to touch it because "Thats IT's responsibility".

So what I am thinking is an AP4421 for the smaller UPS's  4423's for the larger.  Then I use the output from the ATS to power either a SMX1500RMI2U or SMT2200RMI2U for the larger.  I then output the UPS power back into the second power input on the ATS?  That way if the UPS stops outputting power for any reason it will default back to the mains unprotected power, until we get the problem with the UPS resolved.  The UPS's have NMC's so we will be aware immediately that there is a problem.

The loads on these UPS's aren't large generally 1 or 2 Cisco switches with 715watt power supplies.

Is this possible? 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 4423
  • ap4421
  • ats
  • automatic
  • SMT2200RMI2U
  • smx1500rmi2u
  • switch
  • transfer
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

You are asking the ATS to supply the UPS and the UPS to supply the ATS input B. So when the mains fails (Input A) the UPS will be supplying its own input. I don't think that's going to do what you think it's going to do.

In fact, I suspect it'll be a pretty neat oscillator as the UPS jumps back and forward off battery. Next time I'm playing around I must try that and see what happens.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

I have an AP7721 after an SUA3000. The UPS plugs into input A and a direct lead to the mains into input B. The PDU is on the output of the ATS.

If the UPS fails, it automatically switches over. I did it primarily so I could take the UPS out for service as I don't have a bypass panel but it also doubles to protect against UPS failure.

I can't quite get my head around your description as you seem to want to feed the output of the ATS into the UPS. I'd have thought you'd want that powering your load.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

Thanks Brad

The problem I have is that I only have one power source nearby which is a 16amp commando.  Getting another commando at that location is difficult.  The cabs are in a warehouse location.  

So your last sentence is correct really.  Input A is fed from the 16amp commando, the output of the ATS then feeds the UPS, the output from the UPS then feeds Input B.  So in the event of a power loss from input A, power will be supplied by the UPS on input B.  In the event of a UPS failure which would feed input B it would switch to input A with no drop of power.

It's a bit convoluted... but it's the only way i see working with only one power supply nearby.

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:18 AM . Last Modified: ‎2024-03-15 05:42 AM

You are asking the ATS to supply the UPS and the UPS to supply the ATS input B. So when the mains fails (Input A) the UPS will be supplying its own input. I don't think that's going to do what you think it's going to do.

In fact, I suspect it'll be a pretty neat oscillator as the UPS jumps back and forward off battery. Next time I'm playing around I must try that and see what happens.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

Ah yes of course it will... Didn't think of that!  I knew it sounded dodgy when I thought of it, I just couldn't work out why at the time.  Thanks Brad!

I have just thought of another solution though.  16amp Commando splitter cable so one to ATS, one to UPS then UPS to input B.  That should work. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

Hey Matt,

One thing to look out for is that ATSs only support online UPSs but the two models you mentioned above are line interactive UPS.

The ATS may be damaged if used with a line interactive model due to switch thrashing at fail over. 

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of